Been to a property for yet another PIR yesterday and would like to guage other peoples opinion on this one.
Incoming NIE supply cable is supposed to be TNS but the earth at present is fed from 2 951 bonding clamps. My query is on this i have now been advised by NICEIC to fail the installation as its code 2.
I must now report to customer that it fails and to fix this i have been advised to install earth rod and make it TT, this means yet another RCD up front as there are two metalclad consumer units in the premises. Then inform the customer to contact NIE to have them come out check the supply and if they are happy with a 951 clamp get them to issue this in writing and attach to certificate.
Ze at present 0.13 ohms 1.7KA L-E 2.4Ka L-N
Incoming NIE supply cable is supposed to be TNS but the earth at present is fed from 2 951 bonding clamps. My query is on this i have now been advised by NICEIC to fail the installation as its code 2.
I must now report to customer that it fails and to fix this i have been advised to install earth rod and make it TT, this means yet another RCD up front as there are two metalclad consumer units in the premises. Then inform the customer to contact NIE to have them come out check the supply and if they are happy with a 951 clamp get them to issue this in writing and attach to certificate.
Ze at present 0.13 ohms 1.7KA L-E 2.4Ka L-N