I have recently carried out an EICR on an old building, one of the main DBs is an old Bs3036 board with 3 phases.
When testing Ze i measured 0.06 and a PFC of 3.8ka giving a measured value of 7.6ka (as its 3 phase)
Obviously the fault current is too high for the fuses, but can you take into account the suppliers fuse if a fault of such current were to occur? So the old MEM 3036 board wouldn't have to be upgraded?
Thanks