I have recently carried out an EICR on an old building, one of the main DBs is an old Bs3036 board with 3 phases.

When testing Ze i measured 0.06 and a PFC of 3.8ka giving a measured value of 7.6ka (as its 3 phase)


Obviously the fault current is too high for the fuses, but can you take into account the suppliers fuse if a fault of such current were to occur? So the old MEM 3036 board wouldn't have to be upgraded?

Thanks
 
I have recently carried out an EICR on an old building, one of the main DBs is an old Bs3036 board with 3 phases.

When testing Ze i measured 0.06 and a PFC of 3.8ka giving a measured value of 7.6ka (as its 3 phase)


Obviously the fault current is too high for the fuses, but can you take into account the suppliers fuse if a fault of such current were to occur? So the old MEM 3036 board wouldn't have to be upgraded?

Thanks

The protective device must be able to withstand the fault current where it is installed. Bs 3036 are rated between 1 and 3 KA. I take it as worst case 1KA. If your readings are at DB then the board should be up graded. The suppliers fuse could be much bigger than the bs 3036 allowing high fault current to flow which could lead to fuse exploding.
 

Reply to Bs3036 fuses and high fault current in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top