Oh dear, what was happening hear, how could anyone consider even 0.5 mm² cable with a 3 amp fuse was potential dangerous?
I must admit there does seem to be a difference in some books and paperwork as to what is and appliance and what is an installation, I would have said cooker hoods, extractor fans, boilers, immersion heater, built in cookers and hobs etc were alliances, but it seems building regulations class them as installations as they are fixed to the building.
So if part of an EICR then we most inspect and test them, as with opening a plug if not moulded to check there is a clamp on the flex, you should also open up the appliance to ensure all cables are suitable clamped, however we are told the covers on a boiler are part of the gas tight structure and should only be removed by some one registered as gas safe, so it seems boilers are a special case.
However the EICR had code 4 dropped, it was dropped because there was a problem listing all the non compliance with latest editions, the problem was unless there is an installation certificate for an installations then no tester can know if the design was before or after a change in BS 7671 requirements, so the tester would have to test and inspect as if it was installed yesterday, the result was loads of unnecessary code 4 being raised, not sure if a agree with code 4 going, as I feel the owner needs to know before adding to a circuit for example a RCD will need fitting, but the IET seems to have felt loads and loads of code 4's was not help full so was dropped.
However nothing stopping you recommending fitting of an RCD so that circuits can be altered in the future without problems.
But essentially when we moved from code 1,2,3,4 to C1, C2, C3 then our remit changed and we report on the condition and safety of the installation not as to if it follows current or any other version of BS 7671, hence why professional indemnity insurance is required, your giving your opinion, not that of any publication. The books may guide you as to what is permitted, as lets face it, 230 volt is always potential dangerous, and our insurers may give conditions which could include must comply was a set of rules they feel appropriate. But latest edition of BS 7671 does not really help when the latest edition always starts with the dates to which it covers designs from, so a house where wiring designed in 1965 still does not need an earth to light fittings, or any RCD, if following the wiring regulations, will not say BS 7671 as it did not exist back then.
In this case of course covered by latest edition, however since EICR is not any longer tied to any edition since dropping of code 4, then your looking at danger not if it complies.
So for example if I inspect a property with a type AC 100 mA RCD and a TT supply, and a electric car charging point has been added even a 16 amp one, then does it fail, even with all 30 mA does it fail? As the RCD may not trip due to a fault with the car charging. But hang on back in 1954 when house built and the installation was designed we did not have a RCD, but in 1954 with did not have so many electrical goods, my dad told me how proud he was of the electrics of his new house, as it had 5 sockets, my grand fathers house only had 2. And in my great grand fathers day plugging the smoothing iron into lights was illegal as lights was on a different meter to sockets and you paid less for electric from lights meter. Grandma always plugged iron into lights, there were no sockets in the kitchen.
When the MOT came out, we had a book, and it said what the tolerances were, and I remember a dial gauge on a wagon wheel to measure king pin play, if allowed 1/8" that was limit, never mind if safe or not, but if it was not safe, the Dot could still stop you on way home from test station and issue a GV9, even if it did pass the MOT.
So in theory with a new install some one can follow BS 7671 to the letter, and then some one can come and do an EICR and issue a code 2, as they feel it is potential dangerous even if it follows BS 7671. The reverse is also true, an EICR is not anything to do with BS 7671 it is a personal assessment, OK we are guided by many publications as to what we pass or fail but we are not tied to BS 7671 although we may be tied to what our insurers say.