Hello, I took the opportunity over the lockdown to do 18th Ed course but theres a few bits im struggling with. Because its distance learning, the college i signed up with havent exactly been that helpful. So hopefully someone on here knows the answers!
Its to do with the example working out for the 4kw heating load. On the second part of the that question (determining the size of the CPC) theres a table showing various Conductor CSA's with appropriate Conductor resistance @20 degC. I cant find that table in BS7671! the course narrative says table 52.3 but thats nothing like that one. Am i missing something?
Secondly, using the adiabatic formula, the factor of 1.2 is used in the calculation for the temp difference in conductors. Where is that info as it just seems to have appeared!
Thirdly, and i know this is probably a bit stupid, but for the final calc of earth fault loop impedance, the Ze figure is 0.2. Fair enough, but again, where has this come from?
Thanks in advance for the help!
Its to do with the example working out for the 4kw heating load. On the second part of the that question (determining the size of the CPC) theres a table showing various Conductor CSA's with appropriate Conductor resistance @20 degC. I cant find that table in BS7671! the course narrative says table 52.3 but thats nothing like that one. Am i missing something?
Secondly, using the adiabatic formula, the factor of 1.2 is used in the calculation for the temp difference in conductors. Where is that info as it just seems to have appeared!
Thirdly, and i know this is probably a bit stupid, but for the final calc of earth fault loop impedance, the Ze figure is 0.2. Fair enough, but again, where has this come from?