topcat72

Hi There

If anyone can help in pointing me in the right direction within the regs please.

I am a meter engineer and it has been some time since i have had to refer to my regs book since my test and inspection days.
Surveying a meter installation today i have found 2 x 10mm t&e cables serving a 3 phase isolator,
one from the meter which contains 2 no. live conductors with no cpc and the other from a henly block which contains a live and neutral conducor with no cpc.

Regulation 521.8.1 states that "Each part of a circuit shall be arranged such that the conductors are not distributed over different multicore cables"

Is there a regulation that defines this further, i.e each cable single or multicore must contain a neutral or cpc conductor.

Any information would be greatly appreciated.

topcat
 
you don't have to have a cpc within the cable, like an SWA with seperate CPC is ok. As you have pointed out the situation you have is wrong as you have a circuit split over 2x multicore cables.

But also you have the problem that the insulation of T&E is less than the minimum required for 3 phase 415V
 
you don't have to have a cpc within the cable, like an SWA with seperate CPC is ok. As you have pointed out the situation you have is wrong as you have a circuit split over 2x multicore cables.

But also you have the problem that the insulation of T&E is less than the minimum required for 3 phase 415V



What about having 2 live conductors within one cable, no neutral or cpc, this will offer no automatic disconnection, only short circuit diconnection if the cable were to be damaged.

my question was really was there a more specific regulation about a multicore 3 phase circuit containing a neutral ?
 
What about having 2 live conductors within one cable, no neutral or cpc, this will offer no automatic disconnection, only short circuit diconnection if the cable were to be damaged.

my question was really was there a more specific regulation about a multicore 3 phase circuit containing a neutral ?

The regulation you have quoted is specific! It effectively says that the conductors must be in the same multicore cable and not split up across 2 or more.

You cannot have a regulation which requires a cable to contain a neutral or CPC as it would result in a massive waste of time money and materials in having neutrals in circuits which do not require them.
 
The regulation you have quoted is specific! It effectively says that the conductors must be in the same multicore cable and not split up across 2 or more.

You cannot have a regulation which requires a cable to contain a neutral or CPC as it would result in a massive waste of time money and materials in having neutrals in circuits which do not require them.


ok thanks, i get that, i just thought there was a regulation that said you had to have a neutral or at least a cpc within any multicore cable single or 3 phase

TC
 
I think everyone in the UK seems to be called engineers, from those that repair domestic electrical appliances to gas fitters.... Someone somewhere along the line give them the title of engineer!! First time i've heard of a meter engineer though!! lol!!
 
I think everyone in the UK seems to be called engineers, from those that repair domestic electrical appliances to gas fitters.... Someone somewhere along the line give them the title of engineer!! First time i've heard of a meter engineer though!! lol!!

I watched an episode of Watch-dog about 3months ago. It was about a company who repair Hoovers, nothing more, nothing less.

The hidden camera's caught the bloke coming too the house with a younger lad ... the home owner asked some basic questions - are you here to fix the hoover ect... and he introduced himself as the head enginner and the other lad was the apprentice ... apparantly, theirs more too hoover's than meets the eye if it requires apprenterships and head engineers.
 

Reply to BS7671 Multicore cables. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
931
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I’m sure I’ve seen an LSF round cable used on sites before as well with an insulated earth. Not flex, something a bit more substantial but not FP...
2
Replies
21
Views
3K
  • Question
When you did the further testing and got the 0.06 reading were the CPC's back in the consumer unit? Really when testing you should leave the...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top