If anyone can help in pointing me in the right direction within the regs please.
I am a meter engineer and it has been some time since i have had to refer to my regs book since my test and inspection days.
Surveying a meter installation today i have found 2 x 10mm t&e cables serving a 3 phase isolator,
one from the meter which contains 2 no. live conductors with no cpc and the other from a henly block which contains a live and neutral conducor with no cpc.
Regulation 521.8.1 states that "Each part of a circuit shall be arranged such that the conductors are not distributed over different multicore cables"
Is there a regulation that defines this further, i.e each cable single or multicore must contain a neutral or cpc conductor.
Any information would be greatly appreciated.
topcat