Hi
First time with this kind of a job for me.
I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a small metal container housing TPN pump control gear to control two TP 24KW .8 PF pumps (to be fair one is a 15kw, but allowance to swap out one for a bigger one later). Design Current and Volt drop so far state 25mm will be fine.
Because of the distance i would have thought exporting PME would not be a good idea and was going to make it TT as there would be metal railings, the container itself etc. and we are in a very rural area, but...
Speaking with the Pump installers supplying the control gear they do not convert to TT, they always use the earth supplied - but to be fair they are also very close to the supply and have very low ZS.
I have not yet measured the ZS (nor prospective), but i expect ZS will be .2 or above and the supply fuses i am told are 100A, newly installed by DNO. The client took responsibility for this.
First Q, if i am to rely on the suppliers fuses (to protect only the cable between the meter room and the metal cabinet) and install only an isolator at the mains intake to isolate the supply, does anyone have any charts available please that cover Max Earth fault Loop impedance values for the BS88 fuses? Regs book only goes to 63A. BTW the pumps are individually OC protected in the control gear and internal wiring in the control gear to this point is also 25mm.
Also how do i tell what version fuses they are without breaking the seals?
I do not like the idea of leaving the suppliers fuse as the only means of protection for the 50m run of cable into the control gear - it just feels wrong?
I need to confirm but i am pretty sure there is a lockout on the control gear so that both pumps do not start at the same time. So even at 43A (one pump starting) there is a lot of load for about 10 seconds or so TBA.
So if i look at putting in an MCB at the meter end, i need to be sure that they will discriminate (something the pump guys said you will not guarantee even if you had scope to lower the rating of the MCB to 80A) between DNOs and mine and i tend to agree. The pumps, whilst having a slow feature start, can draw a heck of a lot of current on start up, meaning that a C Type MCB maybe the only reliable option, even assuming that the pumps do not start simultaneously. .22 Max ZS for a 100A Ctype, so an MCB may not be an option anyway, may already be too high for the length of riun and Ze. So if cannot discriminate or be selective, what is the point of having additional OC at the meter - that is my thinking. If worst happens and there are issues, i can leave BS88 fuses on site to replace any that go. If they do go though, that's going to be one hell of a fault or lightning strike most likely needing more than just a fuse...
So assuming the maz ZS for the 100A 88 fuses is greater than that measured at the end of the cable supplying the isolator for the control equipment, then TT would not be needed. If the max ZS was lower than the calculated value, and increasing the cable size was not practicable, then I will have to make it a TT and supply a 100mA S type RCD when it comes into the cabin, disconnecting PME and staking it.
Welcome yo ur thoughts please.
Thanks.
John
First time with this kind of a job for me.
I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a small metal container housing TPN pump control gear to control two TP 24KW .8 PF pumps (to be fair one is a 15kw, but allowance to swap out one for a bigger one later). Design Current and Volt drop so far state 25mm will be fine.
Because of the distance i would have thought exporting PME would not be a good idea and was going to make it TT as there would be metal railings, the container itself etc. and we are in a very rural area, but...
Speaking with the Pump installers supplying the control gear they do not convert to TT, they always use the earth supplied - but to be fair they are also very close to the supply and have very low ZS.
I have not yet measured the ZS (nor prospective), but i expect ZS will be .2 or above and the supply fuses i am told are 100A, newly installed by DNO. The client took responsibility for this.
First Q, if i am to rely on the suppliers fuses (to protect only the cable between the meter room and the metal cabinet) and install only an isolator at the mains intake to isolate the supply, does anyone have any charts available please that cover Max Earth fault Loop impedance values for the BS88 fuses? Regs book only goes to 63A. BTW the pumps are individually OC protected in the control gear and internal wiring in the control gear to this point is also 25mm.
Also how do i tell what version fuses they are without breaking the seals?
I do not like the idea of leaving the suppliers fuse as the only means of protection for the 50m run of cable into the control gear - it just feels wrong?
I need to confirm but i am pretty sure there is a lockout on the control gear so that both pumps do not start at the same time. So even at 43A (one pump starting) there is a lot of load for about 10 seconds or so TBA.
So if i look at putting in an MCB at the meter end, i need to be sure that they will discriminate (something the pump guys said you will not guarantee even if you had scope to lower the rating of the MCB to 80A) between DNOs and mine and i tend to agree. The pumps, whilst having a slow feature start, can draw a heck of a lot of current on start up, meaning that a C Type MCB maybe the only reliable option, even assuming that the pumps do not start simultaneously. .22 Max ZS for a 100A Ctype, so an MCB may not be an option anyway, may already be too high for the length of riun and Ze. So if cannot discriminate or be selective, what is the point of having additional OC at the meter - that is my thinking. If worst happens and there are issues, i can leave BS88 fuses on site to replace any that go. If they do go though, that's going to be one hell of a fault or lightning strike most likely needing more than just a fuse...
So assuming the maz ZS for the 100A 88 fuses is greater than that measured at the end of the cable supplying the isolator for the control equipment, then TT would not be needed. If the max ZS was lower than the calculated value, and increasing the cable size was not practicable, then I will have to make it a TT and supply a 100mA S type RCD when it comes into the cabin, disconnecting PME and staking it.
Welcome yo ur thoughts please.
Thanks.
John