can anyone tell us the short circuit capacity rating of a bs88 type 2 fuse.

suppliers fuse was recorded on a old test form NAPIT but dont state the short circuit capcity in Ka.

another quick question when calculating prospective fault current can the formular be used on all types of supplys
pfc=230/Ze
 
As far as I understood it BS 88 Parts 2 or 6 is 80KA breaking capacity. BS 1361 type 2 is most common for domestic @ 33 KA. BS1361 type less common is 16.5 KA. I have come across all three in domestic installations. BS88 fuses can be and are used as main fuses in dom inst.
 
Very good point. Or when it is in an unmarked, sealed carrier? Perhaps when no information is present and the supply company can give you no answers without a ÂŁ100.00 site visit worst case scenario should be adopted i.e. least possible breaking capacity recorded ?
 
good point. anyone know the capacity of a 4" nail. came across this a few weeks ago at a customer who had been cut off. needless to say, i walked
 
which brings me to a question. how can one tell whether the fuse is BS1361 or BS1361/2 when nothing can be read on the fuse itself?

I asked exactly the same question of my college lecturer last week, with one such fuse in my hand (who is by the way a long time served industrial spark who has found an easier way to earn a living :cool:)

The answer I got was that it was really irrelevant (domestically speaking) as whether it was a type I or type II, as by putting 16kA, it would more than cover the short circuit capacity that could occur - as the scc is limited well below this by the characterists of the supply transformer.

So 16kA is going on my forms from now on.....:D
 
Last edited by a moderator:

Reply to bs88 type 2 fuse in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
801
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
833

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top