T
Trulyshocking
Hi,
I'm lucky enough to have been charged with the responsibility for doing all the LPS testing at an MOD base that I work at :frown2:.
Having done the testing, I've had to fail a number of earth electrodes as they measure too high a resistance (in other words above the number of electrodes on the system x 10 ohms). The site includes explosive storage facilities so I want to get it right!!! The question i have is whether or not it is acceptable to douse the temporary test probes (am using a Fluke 1654B) with water to get a better reading. Obviously this cant be applied to the electrode under test!!! The surrounding ground is chalk which doesn't help, but am keen to avoid causing lots of cost in upgrading the buried earth ring if necessary!!
Cheers
I'm lucky enough to have been charged with the responsibility for doing all the LPS testing at an MOD base that I work at :frown2:.
Having done the testing, I've had to fail a number of earth electrodes as they measure too high a resistance (in other words above the number of electrodes on the system x 10 ohms). The site includes explosive storage facilities so I want to get it right!!! The question i have is whether or not it is acceptable to douse the temporary test probes (am using a Fluke 1654B) with water to get a better reading. Obviously this cant be applied to the electrode under test!!! The surrounding ground is chalk which doesn't help, but am keen to avoid causing lots of cost in upgrading the buried earth ring if necessary!!
Cheers