Has anyone created a compacted version of the key points from the building regulations, that are likely to get asked during an assessment?
If so could you show me where it is please.
 
I wrote this before the update of the BR that may be of use, not specifically the questions asked just a ready reference of key points. Not much about Part P because we all already know that!
I do not claim that it covers everything or is currently up to date but there should be few changes apart from the notification bits, afaik.
Building Regulations Parts Applicable to Electrical Work

Part A - Structure
Vertical chases < 1/3 of wall/leaf, Horizontal chases <1/6 of wall/leaf, Chases not damaging wall

Notches in joists between 0.07 to 0.25 of span <12.5% of thickness
Holes in joists between 0.25 to0.40 of span <25% of thickness, Holes to be >3 o.d. apart

Part B – Fire Safety
Positioning and requirements for smoke and heat alarms.
Penetration of fire compartments and the maintenance of the fire resistance rating.
Penetration of fire resistant barriers and maintenance of resistance rating.
Fire stopping of cable penetrations.
Prevention of the spread of fire.

Part C - Resistance to the spread of contaminants and moisture
Prevention of water / contaminants from entering through external cable penetrations.
Prevention of water entering other areas from wet rooms.

Part D cavity insulation
Not normally applicable

Part E – resistance to the passage of sound
Maintenance of the sound resistance properties of walls and ceilings when making penetrations through sound resistant barriers. Both between dwellings and within dwellings.

Part F – Means of ventilation
Requirements for minimum flow rates in kitchens (60/30l/s), utitilty rooms (30l/s), bathrooms (15l/s) and toilets (6l/s) for intermittent extract ventilation.
Ventilation of rooms without purge ventilation (windows/doors) (15min overrun, no natural light operated by light switch)
Cooker hood heights (450mm-750mm from hob)
Air flow through rooms
Applicability to new and existing dwellings.

Part G – sanitation hot water safety and water efficiency
Not normally applicable

Part H – Drainage and waste disposal
Not normally applicable

Part J – Combustion appliances and fuel storage systems
Not normally applicable

Part L1A – Conservation of Fuel and power in new dwellings
Mainly use of energy saving lighting 75%: >45lm/W (if >5W)
Also external lighting to be photocell + movement sensor controlled or energy efficient

Part L1B – Conservation of Fuel and power in existing dwellings
Mainly use of energy saving lighting in area worked on 75%: >45lm/W (if >5W)

PartL2A and PartL2B Conservation of Fuel and power in new / existing non dwellings
Not applicable to Part P

Part M - Access to and use of buildings
Generally just height of switches and sockets >450mm<1200mm
Consumer units accessible
Accessibility of switches, outlets and controls –Height, labelling, consistent location, visual ease and lack of obstruction. Some exceptions (floor sockets).

Part N – Glazing safety
Not applicable

Part P – Electrical safety
Design, install, inspect and test in accordance with BS7671. Work in accordance with H&S requirements. Notify building control for certain higher risk work, or be member of a self certification scheme.
Definitions of notifiable work.
 
Thanks for that list, a good starter for ten! Pretty much the same now I think, but my assessor was also interested in WHERE extractor fans need to be (eg utilities, en suite, etc where no opening windows), apparantly prefer smokes to be on light circuit now rather than RCBO as a fault is more likely to be noticed by users, energy saving can now use low energy luminaires in standard fittings rather than dedicated fittings. In short. all the info is in the book and on here, you can refer to the book in the assessment, so if you know where to find stuff you should be fine. Good luck!
 

Reply to Building regs key points in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
351
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
899
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

HI, I'm a director of a freehold building which is 4 stories (one flat per storey), with a basement flat with its own separate entrance down...
Replies
0
Views
224
When he bought the bank, they stripped out all the metalwork, iron bars etc for scrap. He was left with the cashier countertops… which have been...
Replies
2
Views
438

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top