hi all
today i was working on a site compound for a major uk builder david wilson homes, i have been told by my site supervisor that all compound instalations need to have a earth spike even when there is a tncs supply availabe with a earth is this correct?
regards
 
TN-C-S should not be used on a building site.

Section 704 of the regs refers, also ESQCR and HSE.

Site buildings can use the system i.e offices, canteens, drying rooms etc but, not temp supplies to plant & equipment.

:)
 
It's all to do with the dangers that exist should the neutral conductor in a PME system go open circuit, and magnitude of the resulting currents that may be present in the earthing conductors and exposed steelwork/services. Also being outside an equipotential zone and impossible to run seperate 10mm bonding conductors to each and every extraneous conductive part thus creating a dangerous PD. Wholly unsafe particularly in area's defined as special locations in BS 7671, building sites are one of those locations.
 
Last edited by a moderator:
It's all to do with the dangers that exist should the neutral conductor in a PME system go open circuit, and magnitude of the resulting currents that may be present in the earthing conductors and exposed steelwork/services. Also being outside an equipotential zone and impossible to run seperate 10mm bonding conductors to each and every extraneous conductive part thus creating a dangerous PD. Wholly unsafe particularly in area's defined as special locations in BS 7671, building sites are one of those locations.

so just for my knowledge what system would be used? TN-S? or TT they are the only ones that would make sense to me given what you have said
 

Reply to building site compound electrical work in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
952
  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
2
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top