Been racking my brains all day and still can't figure out how a 6mm twin and earth has ended up burnt out as though having more current through than should the scenario

8.5kw/h electric shower
6mm2 t&e in trunking on wall
40a MCB with 30ma RCD Protected

The cable burnt at CU end and MCB has scorch marks

I cannot understand how the 8.5kw/h shower which pulls 36.95a at maximum heat protected by a 40amp breaker has scorch marks and the cable burnt, any ideas appreciated
 
The screw had probably seized and the cable welded itself in due to the heat build up, giving the impression that it was ok.
 
Cheers Jason, hadn't thought of that hopefully it is sorted now nice job for a callout on a sunday "i Smell burning from my fusebox"
 
Been racking my brains all day and still can't figure out how a 6mm twin and earth has ended up burnt out as though having more current through than should the scenario

8.5kw/h electric shower
6mm2 t&e in trunking on wall
40a MCB with 30ma RCD Protected

The cable burnt at CU end and MCB has scorch marks

I cannot understand how the 8.5kw/h shower which pulls 36.95a at maximum heat protected by a 40amp breaker has scorch marks and the cable burnt, any ideas appreciated

Your 6mm^ T+E erection method B is rated a 38 amps ................awfully close to that 37amp threshold, all you need is a semi loose connection, and you will start heating up. Change it to 10mm^ if it's in a trunking
 
10mm is great if only the shower switches were designed for it!!! just had to replace a switch, 10mm cable, only one earth term . in switch, impossible to connect all strands, and this was a MK switch!!
 
ceiling mounted pull switch. even the knock-out in the patress was too small to get outer sheths of 2x 10mm thru
 
For 10mm cable ceiling mounted pull switch I only fit the crabtree 50 amp switch. Perfectly designed for 10mm cable. Also when the cover is removed it removes the neon as well. Nice to see something designed with US in mind.
 

Reply to Burnt 6mm twin & earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
831

Similar threads

A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top