Want to gain some opinions on busbars and upstream protection.
situation:
3phase busbar chamber, fed from a switch fuse on a rising busbar system. I'm unable to turn off the switch fuse to see what size fuses are installed as it would kill everything on the busbar chamber, but there's a few DB's and what not on the chamber so I'd guess at min they're 100A in the switch fuse.
A small single phase DB is tapped off the busbar chamber in 6/10mm singles which go straight in to the main switch of the DB which is just a double pole disconnector. The circuits are then fed from the small DB with mcb's 6,10A and a few spares etc.
I'm thinking this is wrong. The fuses in the switch fuse are possibly 100A min, the 6/10mm cable is only rated 40/50A and if something went wrong there's no fuse inbetween, protecting the 6/10mm, to blow. The main switch in the small DB is only a disconnecter and offers no overload protection.
Also, to isolate the small DB you have to shut off the whole busbar chamber. So there is no local isolation.
I thought it was ok to tap off the chamber in a cable that is less than the rating of the fuse before the chamber, if you then had eg. a switch fuse upstream (Eg. after the chamber and before small DB) that would have the correct size fuses in for the smaller cable going off therefore protecting them/limiting what can be drawn through them.
It's been a while since I've had much to do with bubars, it's all MCCB panel for me of late. So I'd just like to get some opinions as to wether i'm thinking along the correct lines or not.
This is also very close to the origin and so the highest PFC I got at the small DB was 10kA. All the mcb's are 6kA.
Any help is much appreciated
Thanks
Want to gain some opinions on busbars and upstream protection.
situation:
3phase busbar chamber, fed from a switch fuse on a rising busbar system. I'm unable to turn off the switch fuse to see what size fuses are installed as it would kill everything on the busbar chamber, but there's a few DB's and what not on the chamber so I'd guess at min they're 100A in the switch fuse.
A small single phase DB is tapped off the busbar chamber in 6/10mm singles which go straight in to the main switch of the DB which is just a double pole disconnector. The circuits are then fed from the small DB with mcb's 6,10A and a few spares etc.
I'm thinking this is wrong. The fuses in the switch fuse are possibly 100A min, the 6/10mm cable is only rated 40/50A and if something went wrong there's no fuse inbetween, protecting the 6/10mm, to blow. The main switch in the small DB is only a disconnecter and offers no overload protection.
Also, to isolate the small DB you have to shut off the whole busbar chamber. So there is no local isolation.
I thought it was ok to tap off the chamber in a cable that is less than the rating of the fuse before the chamber, if you then had eg. a switch fuse upstream (Eg. after the chamber and before small DB) that would have the correct size fuses in for the smaller cable going off therefore protecting them/limiting what can be drawn through them.
It's been a while since I've had much to do with bubars, it's all MCCB panel for me of late. So I'd just like to get some opinions as to wether i'm thinking along the correct lines or not.
This is also very close to the origin and so the highest PFC I got at the small DB was 10kA. All the mcb's are 6kA.
Any help is much appreciated
Thanks