hi all, if youre doing a c/u change and you do a survey first and the kitchen is a old single storey extension, with no accsess at all to the roof space but there a 4 downlightlers which when you remove you can see insulation but can't see proper to work out the depth would you apply method 101 to be on the safe side, problem being there is a 6mm cooker cable there and method 101 would take the cable to 27A meaning mcb would have to be 20A,checked cooker and its only 2.2kw (9.6A) so 20A mcb is no probs but the cooker switch as a plug outlet which according to the regs on diversity is to add 5A still within the limits but just concerned if say they bought a 3kw kettle and used it in the cooker socket and have cooker on full and make a brew it is going to be drawing more than 20A and obviousy trip,but if i was to use method 100 then a 32A mcb could be used, would you always use the higher method with the lower A rating to be safe,
next question each ceiling rose as only 1 t&e coming into it,normal j/b under floorboards,would all these have to be changed to m/f j/bs before you could do the c/u as they do not comply with the regs as they are cheers
next question each ceiling rose as only 1 t&e coming into it,normal j/b under floorboards,would all these have to be changed to m/f j/bs before you could do the c/u as they do not comply with the regs as they are cheers