After getting a phone call just now, I'm a tad confused as to what this chap is saying !

Q, He has a dis board with buz bar connecting his breakers. He also tells me that his last two breakers (10 amp & 16 amp) are fed from 2.5 singles from a breaker that is connected with buz bar.

Is this within regs ? :eek:
 
After getting a phone call just now, I'm a tad confused as to what this chap is saying !

Q, He has a dis board with buz bar connecting his breakers. He also tells me that his last two breakers (10 amp & 16 amp) are fed from 2.5 singles from a breaker that is connected with buz bar.

Is this within regs ? :eek:

No it isnt. This sounds like 2 breakers have been added to the spare ways but the busbar has been cut short. The busbar needs replacing with one that will connect all the breakers, or alternatively you can get suitable copper links to join the breakers to the existing busbar. If the bubar is a common make like Wylex or MK getting a new one will be easy. I know screwfix do busbars but you may have to file it to make it fit. But 2.5mm is a definite non no on the supply side of the breaker unless the PFC is below about 20a which i doubt.

Cheers.........Howard
 

Reply to C/Unit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
564
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
998
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
937

Similar threads

I'm begining to think like this now, I very rarely work for builders anymore but the couple that I still do work for are the worst payers out of...
    • Like
    • Agree
Replies
8
Views
779
  • Question
Why not fit a self contained SPD fed directly from the Henley blocks, and free up a bay? Could probably make one up from whats there, using a...
2 3 4
Replies
47
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top