no code , IMO. a comment on the cert. might be appropriate.
 
Regs book and OSG are in the van and I'm inside but at the beginning of the OSG there's a picture of a gas meter and I'm sure it says electrical cables need to be 25mm from pipes and outlets/CCU needs to be 150mm from gas and water services (gas meter and stopcock)
Also I do a lot of maintenance work for councils and the supervisor always makes me move outlets to 150mm when I report back after a test.
 
The OSG reminds you of the regulations regarding separation from gas not water.
150 mm from gas meter
25 mm from gas pipework.
(If you ever see this done then let me know)

Tel as usual has summarised it in a nutshell.
 
How high is the stop-cock? How low is the socket outlet? Full information req'd. RCD protected?Radial? Ring? Size of cable? Everything ok C3,any defects,C2.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London

Thread Information

Title
C2 or C3
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
12

Thread Tags

Tags Tags
None

Advert

Thread statistics

Created
Prime Design,
Last reply from
2391bob,
Replies
12
Views
2,018

Advert

TrueNAS JBOD Storage Server

Back
Top