Ring main was on a c40 rcbo so I tested the circuit everything was fine and dropped down onto a b32, It’s quite a long circuit but only serves about 10 sockets.The rcbo stays on but the client says trips frequently, I’ve been back and the rcbo stayed on the whole time, I then left and over the weekend it has tripped again but went back and all stayed on fine the whole time I was there again. Type c is for higher inrush but there’s nothing on circuit which would cause this… any ideas would be appreciated. 👍
 
This has all the hallmarks of an original design of a 32A OCPD being swapped out to a 40A one to 'solve' the problem that the OP now has.

If you have sufficient sized cable and a low enough Zs to satisfy the 40A (without relying on the 1667Ω of the RCD!) then I'd swap back - something about if it aint bust don't fix it!
 
This has all the hallmarks of an original design of a 32A OCPD being swapped out to a 40A one to 'solve' the problem that the OP now has.

If you have sufficient sized cable and a low enough Zs to satisfy the 40A (without relying on the 1667Ω of the RCD!) then I'd swap back - something about if it aint bust don't fix it!
Hi thanks for reply, I need to make alterations to the circuit also so just wondered what could possibly be causing the breaker to trip maybe from others experiences, seems another sparks just whacked it on a c40 to stop it from tripping.
 
Hi thanks for reply, I need to make alterations to the circuit also so just wondered what could possibly be causing the breaker to trip maybe from others experiences, seems another sparks just whacked it on a c40 to stop it from tripping.
Two reasons for the trip - either overload (/inrush) or earth leakage. A clamp meter will help with the first and a full IR test the other. You say it’s ‘quite long’ - that always makes me suspicious of a joint or other connection somewhere that you haven’t found yet. An R1R2 measurement will help you know exactly how long (look up the resistance values in the OSG and do the maths). Also, does the circuit hold with zero appliances connected? Again, that splits it down to either the installed circuit or a faulty device.
 
You might be able to get some useful data out of the client. It has been known!
Does it trip when he turns something on, or at certain times of day, or completely randomly when the circuit isn't in use much?

You could try a ramp test with the loads plugged in and see how close it is to tripping all the time.
You say it tests out ok, so one would err towards an issue with a load not the fixed wiring.
 
You could try a ramp test with the loads plugged in and see how close it is to tripping all the time.
Another useful step at that stage is to use a mA sensitive clamp over the cpc at the origin of the circuit and see what leakage you have initially, I'm always slightly sceptical of the ramp test method if you don't know enough about the circuit to start with and there may be alternative paths to earth.
 
Two reasons for the trip - either overload (/inrush) or earth leakage. A clamp meter will help with the first and a full IR test the other. You say it’s ‘quite long’ - that always makes me suspicious of a joint or other connection somewhere that you haven’t found yet. An R1R2 measurement will help you know exactly how long (look up the resistance values in the OSG and do the maths). Also, does the circuit hold with zero appliances connected? Again, that splits it down to either the installed circuit or a faulty device.
Thought it was inrush at first but only a tv and couple of lamps plugged into the circuit at the moment. It held with nothing plugged in but couldn’t wait around all day as clients quite a pain!. It also holds with loads in and trips unannounced not when client turns something on etc which is usually the problem. Thanks for reply
 
Thought it was inrush at first but only a tv and couple of lamps plugged into the circuit at the moment. It held with nothing plugged in but couldn’t wait around all day as clients quite a pain!. It also holds with loads in and trips unannounced not when client turns something on etc which is usually the problem. Thanks for reply
Is this domestic or commercial? My first thoughts are wondering if there’s a timer involved somewhere which makes me think if this is domestic has a heating system been spurred off somewhere?
 
This has all the hallmarks of an original design of a 32A OCPD being swapped out to a 40A one to 'solve' the problem that the OP now has.
Indeed!
If you have sufficient sized cable and a low enough Zs to satisfy the 40A (without relying on the 1667Ω of the RCD!) then I'd swap back - something about if it aint bust don't fix it!
Trouble is if this is a domestic RFC in 2.5mm then pushing it to 40A is not a good idea due to CCC.
 
Is this domestic or commercial? My first thoughts are wondering if there’s a timer involved somewhere which makes me think if this is domestic has a heating system been spurred off somewhere?
I was wondering the same.

As an RCBO it can trip for one o(or more) of 3 reasons:
  • Too much leakage
  • Too high inrush
  • Too high load
If you cant find any big loads to explain things, it is either a leak or an intermittent fault. If going 40A C "fixed" it then load/inrush is expected, unless the RCBO was stick and only after testing/cycling and eventual replacement is the leak being spotted!
 
This sounds to me like the equivalent of thick aluminium foil wrapped around the fuse in a 13A plug! A domestic RFC, not serving a kitchen, should normally be happy on a B16. If a C40 is tripping on the MCB part, then something needs urgent investigation.
If it's tripping on the RCD part, then equally it needs urgent investigation.
 

Reply to C40 rcbo on ring main changes to b32 causing nuisance tripping in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
289
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
792
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
822

Similar threads

  • Question
My thoughts exactly! Snowed under with work at the moment, so might have to pass it on 😬😬
Replies
4
Views
2K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top