Cable calc for meter tails?!! | on ElectriciansForums
Discuss Cable calc for meter tails?!! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
U
ukpablo
ok, need a lil help.
Cu approx 40 metres from meter.
in a block of flats.
total demand is 132A therefore after diversity
132A x 0.4 = 52.8 A (approx)
cable run in tray in cable duct in free air.
100A cutout fuse in place at mo. currently in 25mm armoured! is this enough?
lil rusty on this one as this is a sub main cable so is there a difference?
I know this isn't the technical answer you wanted, but I would say 25mm2 (as 40m run) armoured on 63A fuse/MCB would be enough for any flat I have ever been to.
As for diversity, I think there is more common sense than calculations required.
I have just read the post again and am unsure of the situation.
How is it 132A x 0.4 because as far as I know there is no set rule for diveristy like that, it works like 100% of 1st shower and then 30% after, and 100% of socket circuit and then 10% after, etc
don't think current load is a problem. be more concerned with calculating volt drop
i used 1.2 multiplying factor as one should
40x52x(0.72+0.72)x1.2 / 1000 = 3.6 volts
but i would be interested in the calc provided by your software
thanks
I get 3.64v drop on 25mm, 40M run, in a void, multicore General PVC cable on a 63A but with 52A load - using cable-mate programme.
Reply to Cable calc for meter tails?!! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net