Cable calc min CPC | on ElectriciansForums
Discuss Cable calc min CPC in the Australia area at ElectriciansForums.net
hi there
can anyone just check my use of adiabatic please
4mm/1.5mm cpc circuit, type 2 30A MCB
zs = 0.35
pfc = 230/0.35 = 657.14
t = 0.01
k= 115
s = sqroot (657.14x657.14x0.01)/115
= 0.5714 mm
so the 1.5mm cpc will be fine. Yes ??
Carefull hospital table 41.1 is for maximum disconnection times in TN &TT systems.
If you were to use the 0.2 secs have another look at the maths!
Ian you calcs look OK its just I don't have access to the time current characteristics for a 30 A mcb type 2.
Looking at the OSG I see the ZS is 0.88 ohms 230/0.88 = 261 A so your 657 A should disconnect in 0.01
No doubt another member will come on who has the time curves.
Regards
Tony
Your calculation and conclusion is correct Ian. For the BS 3871 Type 2 MCB time/current characteristics you will need to refer to a copy of 16th Edition of the Wiring Regulations as they are not in the 17th BRB or BGB as BS3871 is a withdrawn standard replaced by BS EN 60898.