Would one of you helpful chaps do a cable calc for me, as i dont have my books to hand at the moment as i am away.

40A over 100 meters. Most of it SWA.

Much obliged :)
 
I got 16mm cable :confused: the ccc will be 91V and your VD would be 11.6V so just borderline @ 5.04%

I calculated that on 10mm cable the VD would be 18.8V which is 8.17% (above the 5% allowance)

Hope this helps
 
Last edited:
I got 16mm cable :confused: the ccc will be 91V and your VD would be 11.6V so just borderline @ 5.04%

I calculated that on 10mm cable the VD would be 18.8V which is 8.17% (above the 5% allowance)

Hope this helps

Please correct me if I have this wrong, but with a VD of 11.6/ 5.04% this will not leave any allowance for any lighting to be installed in the office as the max permissible VD for lighting is only 3%. It is also on the limit for power circuits and this is only the supply to the dis board (without circuits installed).
 
Last edited:
Please correct me if I have this wrong, but with a VD of 11.6/ 5.04% this will not leave any allowance for any lighting to be installed in the office as the max permissible VD for lighting is only 3%. It is also on the limit for power circuits and this is only the supply to the dis board (without circuits installed).

I used a total design current of 40A including power and lighting! So what would you suggest then possibly take it one up to 25mm? :confused:
 
I used a total design current of 40A including power and lighting! So what would you suggest then possibly take it one up to 25mm? :confused:
I see what you are saying. TBH I didn't do any calcs I just saw the 5% Vd and I am a bit unsure as to how the 3% for lighting affects the calcs. I will do the calcs etc as I would do them inc VD for the ccts, and post them up for people to look over and pick holes in etc. I may be some time!!
 
I used a total design current of 40A including power and lighting! So what would you suggest then possibly take it one up to 25mm? :confused:

The way I have always done it is to calculate the VD & CCC for the cable up to the office with a design current of 40A. I would then design the circuits in the office seperately so 3% for lighting and 5% for power. Hope that makes sense?:D
 
ok peeps here is the situation.

I have roughly estimated a 40A submain for a garden shed office.

Its only going to have a few PC bits and pieces, lighting and more than likely a panel heater.

I have in mind a 40A MCB radial, although im sure a 32A would suffice.

Basically, i dont really want to have to run 16mm SWA :D
 
Ah well, 16 it is then.

Mind you, i might be able to persuade him to move it up the garden a bit and try to reduce the run.

That is one trench i will NOT be digging :D
 

Reply to Cable Calc. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
919

Similar threads

OK, thanks, I see the speaker now. I imagine it's 'home-made'. If the modules you mention are powered directly from the mains supply, their...
Replies
7
Views
491

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top