Hi guys im having a brain storm of absolute brain death.

Fire alarm Loops of around 600m and 500m Give or take FP 200 1.5mm (1100m Total cable not accounting for Cutting to much cable etc)

My problem is this, the 2 Loops of cable gave me a resistance Value of about 3.07ohms cpc to cpc and 2.93ohms cpc to cpc respective, but i would expect a larger Figure than this as the total cable use would be 1000m ish of cable, BGB 12 for it FP200 cable mv/per/m etc as im sure im not thinking straight.

Im getting like 2/3 hundred meters lmao so help defo would be very helpfull...

No other connections to earth are there only two loops as yet, but will be adding to 230 Earthing due to tranformer/contactor, cables etc...

Thanks guys catch you L8r
 
If you are measuring the cpc on FP200 cable the cpc is in contact with the aluminium screen (which is a minimum of 0.075mm thick) the combined resistance of the cpc and the screen would therefore be about 2/3 of the value for just the cpc, so from OSG 12.1mohm/m is now 7.75mohm/m.
I would get 4.65 ohm and 3.87 ohm for the 600m and 500m cables.
But if the screen is say 0.12mm (me attempting to measure it with a very poor caliper!) the resistance would be about half the expected value, which is what you got.
Compare with your line and neutral end to ends and see if they about twice as high.
 
So what you are saying is that the end to end on the earth core is reading lower than you would expect for its csa, 1.5 or whatever?
Are you not then getting assistance in the ohms department from the ally sheath?
It may be touching/making contact with the bare earth at some/many points.
Also if you are using metal boxes fixed to steelwork the ally sheath may then also be touching the boxes in places?

Boydy
 
Thanks guys this is what i was missing the foil the reading is defo on about par with the readings you have mentioned, the reason for not mentioning the Phase and Neut was because they are not in a loop like a ring only the Earth was a Loop, being a Analogue System (Addressable..(NOt continues through the devices))..

Yes boydy the reading was lower than i thought, but now with the guidance makes a lot more scence..
 

Reply to Cable Calc ? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

  • Question
hi yes sorry its just cos i copyed and pasted it from the one above as that was for the lighting
Replies
4
Views
1K
  • Question
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
    • Like
Replies
0
Views
2K
  • Question
Thanks a lot, that is very helpful. I will do some calcs to work out the earth cable size. I've replied in detail above to the other chap "Lucien"...
Replies
4
Views
3K
  • Question
I assumed this but as the load is not apparent I cannot make the best guess to it even do you mean the 0.86 multiplier after i search ill pick...
Replies
7
Views
2K
  • Question
A fault that is going to blow the 80A fuses is also likely to blow the 100A fuses you get no realistic discrimination . There's no point in...
Replies
53
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks