Hi guys just looking for a bit of help / advice

i have a 100amp 3 phase isolator tap off connected to a rising bus bar.

im installing a new 16 way 3 phase DB approximately 55 metres away from the isolator.

it will be wired in 4 core armoured on tray, and on its own located with in a ceiling void.

the electrical consultant has indicated to use a 50mm 4 core armoured, I think a 35mm would be fine.

Can any body point me in the right direction for the correct calc?
 
Try your normal calcs mate, although I'm not sure why you're querying it. It'll be the consultant signing off the design.
You could always give the gadgie/wifey a ring and talk through the calcs.
 
Hi trev

the run is a nightmare and would make it a lot easier with a 25mm/35mm armoured.

not really up to date with my calcs, once I get the bread and butter of it i suddenly remember. But then usually forget it a few months down the line
 
So how did you come up with 25/35mm swa mate?
Think logically and it'll all come back to you.
In no particular order=
CCC
VD
Temp
Grouping
Etc
Etc
 
I would go with the consultants sizing without a query. He will have allowed for the adequate VD from source to final circuit rather than just this sub.
 
it'll work out at less than 25mm if you calculate it for 2 x cables in parallel, 2 x 16mm is more likely but I wouldn't be too surprised if it came out at 2 x 10mm
 
Surely 35mm would do it, 50 does seen quite a bit overkill but I guess the main factor affecting it will be from where its fed from.

like many others have said unless you go for a bigger cable it might not comply with tripping times
 
If this is a specified job/project then you, or your company have signed a contract to provide the electrical installation based on the project drawings and specifications. Any deviation from either of those contract documents without prior permission from the ''Engineer'' and you'll be in a S**tload of trouble!! As already suggested, you could seek permission to use a parallel supply of a suitable size if the routeing of this sub main is is going to be a real hassle with a 50mm 5 core SWA.
 

Reply to Cable calc?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
912

Similar threads

The total current capacity of the system in amperes is the same as the per-phase rating when referring to a balanced three-phase system. Thus, a...
Replies
4
Views
654

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top