Hi,
Calculating - for the first time - SWA buried cable.
The design current (Ib) is 12 amps
The cable run will be 20 metres, buried in the ground.
I'm looking at 2 core SWA, using the armour as earth
(no grouping, ambient temp changes (other than buried) or rewireable fuse factor to consider)
I'm going to join the home (Zs's permitting) off the downstairs ring main (RCD'd) with a external fused spur at 13 amps (so In =13a).
Now this is the fuzzy bit... do I
1. look at tabulated current (It) based on the 2 core Multicore Armoured - Ref Method D (P147 of unite book) to see that 2.5mm works (up to 29 amps?) and doesn't suffer from excessive volt drop (18x20x12/1000=4.32v, well within 5%)
or
2. look at 4B3 on page 128 to calculate factor in which case I have no idea of k.m/w!
I've assumed it's the former, but given the higher ampage than 2.5mm T&E I'm suddenly wary.
(Yes, this cable calc business is so much easier with a tutor standing close by!)
Any help/thougths on these cable calcs would be appreciated.
Calculating - for the first time - SWA buried cable.
The design current (Ib) is 12 amps
The cable run will be 20 metres, buried in the ground.
I'm looking at 2 core SWA, using the armour as earth
(no grouping, ambient temp changes (other than buried) or rewireable fuse factor to consider)
I'm going to join the home (Zs's permitting) off the downstairs ring main (RCD'd) with a external fused spur at 13 amps (so In =13a).
Now this is the fuzzy bit... do I
1. look at tabulated current (It) based on the 2 core Multicore Armoured - Ref Method D (P147 of unite book) to see that 2.5mm works (up to 29 amps?) and doesn't suffer from excessive volt drop (18x20x12/1000=4.32v, well within 5%)
or
2. look at 4B3 on page 128 to calculate factor in which case I have no idea of k.m/w!
I've assumed it's the former, but given the higher ampage than 2.5mm T&E I'm suddenly wary.
(Yes, this cable calc business is so much easier with a tutor standing close by!)
Any help/thougths on these cable calcs would be appreciated.