hi, I'm trying to work out which cable size to use for a cooker but I'm not sure what the ambiant temp will be for the correction factor can any one help please?
 
Still learning - are you asking about temperature because you're thinking about the cable that goes from the wall to the cooker?
 
i would work out the diversity first. if , say, the current demand was 32A ( after diversity ) and you decided to use 6mm cable clipped direct, that is rated at 47A, so i would not even bother with correction factor, as the 6mm is well over demand. ( unless this is an exercise for college, then you need to calculate it ).
 
Cookers are often a suprise, after the initial shock of reading the "28.7Kw total load" on the back, when you work it out by the book it comes out not needing much at all.
 
hi, sorry to bother you again but can I run my calcs by you to check if I done it right.
cooker is 10.6kw

10600/230 = 46A

10 A
+ 30% (10.8A)
+ 5A

= 25.8A
which is 2.5mm clipped direct as it has a rating of 27A
 
Your forgetting the protective devise your intending to use. In any case, It's good practice to keep domestic cooker type circuits on a minimum 6mm cable....
 
25.8A is pushing 2.5mm. definitely go for 4mm, or as engineer has said , 6mm. you never know if a larger cooker may be fitted in the future. so 4mm or 6mm on a 32A MCB.
 

Reply to cable calcs for cooker in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
436

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top