i'm doing the 2391 course not sure about a way we have been shown with regards to rewirable fuses (not quite how i remember 20 years ago) heres the example -
7000 watt heater to be covered by a rewirable fuse
current is 30.43 amps, fuse will need to be 45a
now he has applied the correction factor to this (not to the design current)
so
45 / .725 = 62.07 amps, cable needs to be 10 mm (twin)
is this right? i always thought we applied fuse correction to design current
so
30.43 / .725 = 42 amps, still go with a 45 amp fuse but using 6mm cable
i know i'm probably wrong, just want to make sure