Well in order to derate a cable you would first need to work out which factors applied in a given scenario, i.e ambient temperature, grouping, thermal insulation, protection by a BS 3036 fuse (Ca, Cg, Ci, and Cc respectively)

Obviously calculate design current (Ib) select protective device rating (In) then apply factors to tabulated CCC (It) to obtain CCC of cable in particular service conditions (Iz).

Another way is to apply any factors to (In), then select a cable with an (It) greater than (In).
 
Last edited by a moderator:
for example i am fitting an outside light under a plastic lean-to, I am using a 6 A fuse in the CU, the cable run is 6 metres, the ambiant temperature during the day will be high but at night when the lights are to be used will be cooler say 15 - 20 degree's from this info what would be the calculation to determine cable size?

cheers
 
Well seeing as you already have (In) then any factors you would apply to this, ie - (In)/CaxCgxCixCc.

= 6/.........

All the factors you will find in Bs 7671.;)
 
hi, sorry i'm even more confused now. first what does CaxCgxCixCc stand for and to de-rate a cable i was told to / the conductor cross sectional area by the de-rating factor so what do i devide 6 by? and how do i factor the length of cable into it, can you give me an example and then the calculation so i can then apply that to other situations so i can understand and remember how to do it.
cheers
 
suggest you read up its quite long winded
Apply any corrections (for temp, grouping, thermal, fusing ect)
these values are all in brb or osg and will vary depending on installation

above is only one part of the whole design guide.

as im too lazy to type it up:
http://www.tlc-direct.co.uk/Book/4.3.9.htm
 
Last edited by a moderator:
hi, thanks i think i'm getting the hang of it i found another thread that explains it a bit i'm just trying to find where i can get the tabulated rated current from to do the calc.
 
so is the tabulated current the size of the fuse or in my case for 1.5 t&e clipped direct the CCC which is 16A and that is timesed by the ambiant air temp derating factor which if i am correct will be 0 because in table 4D5 that is the CCC at 30 degrees. or because it's outside do i have to take anyother factors into consideration.
also i am putting a switch/socket on a garden wall 6 meter run is SWA overkill or a must?
 
While it is great to be able to do the calcs by hand (I have been doing it for about 6 months now) I have just bought off ebay a cable calculation program which claims to be to the 17th and designed by an electrician.

Gonna compare it to what I get and see how it measures up - at ÂŁ12 it's not a lot to lose if its junk!
 

Reply to cable calcs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

totally agree
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top