S

Steve D

Hi All,

I'm rewiring a garage. There is SWA into the garage and I intend to fit a new RCD protected garage CU with 16A & 6A breakers.
Would you recommend putting a 25A or 32A breaker in the main CU ?

I haven't inspected site properly yet but I just had a thought with respect to the existing SWA cable sizing which is currently buried. Am I right to assume that the cable needs to be sized in accordance with the size of the CU fuse? Therefore a 32A breaker at the CU demands that the cable is capable of carrying minimum 32A ?

Excuse my ignorance but I'm never really worked with SWA in the real world before, so what is the difference between tables 4D4A 70C armoured thermoplastic and 4E4A 90C armoured thermosetting? I've got a note in my regs to generally use table 4E4A but naively, I don't really know have to identify what type of SWA exists.
Will there be some sort of code on the external of the cable for me to identify ?

Cheers
Steve
 
The breaker size will be decided by the size of cable u are using because ur breaker is used to protect ur cable . Some S.W.A cables have the size written on them i would generally use a 32A breaker for 2.5 and 4 mm cables
 
Thanks,

With respect to the SWA gland I need for terminating, there are internal & external types. Does this simply mean for indoors use and outdoors use.

When I'm terminating the SWA into my metal CU, and I use a banjo (I think that's the right term anyway!) to link the SWA armour to the CU earth, what size CPC would you normally recommend for this link? Would it be 10mm or would you recommend something smaller.

Apologies for the basic questions, but it's only when you start to do these types of jobs that you see the shortfalls in the college courses - I accept they can't teach absolutely everything, most things will come with experience.

Cheers
Steve
 
Yeah it will just be indoor and outdoor , i tend to use just the external glands

Banjo,s , Frying pans , earth tags , yeah stick one of them on and just use an earth wire the same size as the cores on your S.W.A
 
Hi Steve D


Don't worry about the main isolating breaker in the CU you can leave that at 100A if you want, its the overcurrent protection/fuse you are supplying the submain with you want to rate in line with the size of the submain. To get an idea of the size of the submain you need, or to ascertain if the existing is Ok you need to work out the maximum demand. If you are unsure of the size of cable you need, give us more detail of the run and length and the MD and we can give you a indicative cable size.


The way I usually size SWA's
  1. By looking (sometimes on side of cable) or taking an educated guess..
  2. Disconnecting a core and trying different size lugs to gauge.
  3. Use a vernier calliper.

Regards
 

Reply to Cable Calcs in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
811

Similar threads

A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top