Good Evening Gentlemen,
Please bare with me as I have looked at previous posts and some people have asked similar quistions and got slated for it...
I am wiring an office, it's on the fourth floor of a multi story building! I need to run two supply's to comms cabinets inthe basement. The cable run is under a raised floor so in free air really clipped to the floor! It then jumps into a riser down to the basement on basket on its own again. The overall run is 89 meters my employer seems to think 6mm swa will be fine. And I just wanted to check... I have not worked these figures out in a while but come to the conclusion that I will have 10.39v in my volt drop and rating factors ca = 1. Cg=1. Cf=1. =3 16amp 60898. 16 divide by 3 = 5.33
So could you please guid me whether I am on the right tracks or and if my cables selection is right.....
Many thanks
Please bare with me as I have looked at previous posts and some people have asked similar quistions and got slated for it...
I am wiring an office, it's on the fourth floor of a multi story building! I need to run two supply's to comms cabinets inthe basement. The cable run is under a raised floor so in free air really clipped to the floor! It then jumps into a riser down to the basement on basket on its own again. The overall run is 89 meters my employer seems to think 6mm swa will be fine. And I just wanted to check... I have not worked these figures out in a while but come to the conclusion that I will have 10.39v in my volt drop and rating factors ca = 1. Cg=1. Cf=1. =3 16amp 60898. 16 divide by 3 = 5.33