Good Evening Gentlemen,

Please bare with me as I have looked at previous posts and some people have asked similar quistions and got slated for it...

I am wiring an office, it's on the fourth floor of a multi story building! I need to run two supply's to comms cabinets inthe basement. The cable run is under a raised floor so in free air really clipped to the floor! It then jumps into a riser down to the basement on basket on its own again. The overall run is 89 meters my employer seems to think 6mm swa will be fine. And I just wanted to check... I have not worked these figures out in a while but come to the conclusion that I will have 10.39v in my volt drop and rating factors ca = 1. Cg=1. Cf=1. =3 16amp 60898. 16 divide by 3 = 5.33

So could you please guid me whether I am on the right tracks or and if my cables selection is right.....

Many thanks
 
The PD current has been used here to calculate the volt drop.

But as Davesparks says it is not divide by 3 but by 1 to give a tabulated value of 16 A or less.

6mm² SWA will just about cope with that!

So volt drop OK, current carrying capacity OK.
 
Id be more concerned about the earthing arrangement here been a comm's supply... upgrading the SWA to 4core and larger csa could allow for an extra core to meet the requirements of the functional earthing....

Thats if it is what I think it is?

It be an expensive error to forget the requirements for functional earthing ... again if it is required --- info needed!
 
Last edited by a moderator:
Thanks for the reply's people....

I am gaining access to the comms room tomo so will check the earthing arrangement, but when ever I install power to comms cabinets I run a clean earth back to the incoming earth bar!

Many thanks
 

Reply to Cable calcs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

The power company only brings in 3 wires which is 2 live and 1 neutral wire. It’s our responsibility to add the ground rod to bond the neutral...
Replies
3
Views
613

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top