Trainees, I realise this will probably be a little over what you will have covered (or in fact will cover) in college. I'm hoping that it may open up a new route of thinking how to plan bigger installs.
Mentors feel free to have a bash.
Here's the scenario. (It's from a real job I undertook a few months ago in Russia)
Ok so its for a 640Kw motor, starting method is a soft start inside delta.
FLC is 1100A (I've done the math here for you)
Voltage out there is 380/220v
It's run is clipped direct to tray, with a grouping factor of 0.78
Ze is 0.003
Protected by 1600A MCCB (this is providing short circuit and earth fault protection). The Zs required for the mccb is 0.015.
The Soft start has a built in thermal overload that will be set at 0.58*FLC.
Length of run is 70 meters.
XLPE SWA is the preferred cable type.
I will explain later on how a soft start works inside delta. Treat it as a star delta starter, regarding wiring from the control panel to the motor.
Tony, I know your in here now and you may remember me discussing it with you. Don't give away the answer.
Oh, and no there wasn't any MV on site suitable.
Up for grabs on a correct answer: The electricians bible on motors by Brooke Crompton (there now as rare as rocking horse s***). Some of the older members on here will have been given them when they started their [FONT=helvetica, arial, sans-serif]apprenticeship. [/FONT]
Mentors feel free to have a bash.
Here's the scenario. (It's from a real job I undertook a few months ago in Russia)
Ok so its for a 640Kw motor, starting method is a soft start inside delta.
FLC is 1100A (I've done the math here for you)
Voltage out there is 380/220v
It's run is clipped direct to tray, with a grouping factor of 0.78
Ze is 0.003
Protected by 1600A MCCB (this is providing short circuit and earth fault protection). The Zs required for the mccb is 0.015.
The Soft start has a built in thermal overload that will be set at 0.58*FLC.
Length of run is 70 meters.
XLPE SWA is the preferred cable type.
I will explain later on how a soft start works inside delta. Treat it as a star delta starter, regarding wiring from the control panel to the motor.
Tony, I know your in here now and you may remember me discussing it with you. Don't give away the answer.
Oh, and no there wasn't any MV on site suitable.
Up for grabs on a correct answer: The electricians bible on motors by Brooke Crompton (there now as rare as rocking horse s***). Some of the older members on here will have been given them when they started their [FONT=helvetica, arial, sans-serif]apprenticeship. [/FONT]