Hi
Sorry if I’ve posted this in the wrong area.
Do the tabulated values for the current carrying capacity of conductors in bs7671 include the 1.45 rule of thumb?
I.e. a 32amp type B should trip within an 1hr at 1.45x it’s In (46.4amps)
So do I look for a cable that can take 46.4amps, even if the Ib is only 32amps?
I’m sure I’ve seen a reg that states the 1.45 is satisfied when using the tabulated values for twin & earth.
This is all hypothetical and I’m trying to keep my question simple (leaving out the other correction factors and install method)
Cheers
Sorry if I’ve posted this in the wrong area.
Do the tabulated values for the current carrying capacity of conductors in bs7671 include the 1.45 rule of thumb?
I.e. a 32amp type B should trip within an 1hr at 1.45x it’s In (46.4amps)
So do I look for a cable that can take 46.4amps, even if the Ib is only 32amps?
I’m sure I’ve seen a reg that states the 1.45 is satisfied when using the tabulated values for twin & earth.
This is all hypothetical and I’m trying to keep my question simple (leaving out the other correction factors and install method)
Cheers