Hi please can someone assist me in confirming the correct size for sub board. ( ie ) i have 4 motors rated at 18.5kw feeding each motor individual 16mm swa distance 50mtrs . From supply to d/b 50mm swa 100mtrs protected by 200a if full load was to be used. any thoughts appreciated
 
would also need more info' as regards to motors ... are they running high inertia loads the frequency of start, dol or star/delta or do you have soft start in place like inverters to name a few things, and regarding cale size and length you havent told us the environment the install method, the type of fusing device etc etc.....
If you can appreciate you have given us little to go on so more info please just so your post can be answered with a little accuracy.
 
I think the volt drop would be too great on the length and CSA of the cables you are proposing for the connected load
 
Think you would be looking at 70.0mm xlpe/swa at least as 50.0mm not rated at 200A, table 4E4A in BRB, but as stated more info is required for a better answer
 
Hi sorry about lack of info, hope this helps. ok 4 motors 18.5kw 50hz ( swa 50mtrs running under ground ) ( star/delta ) (30 hp) (3ph 380v ) (eff 90% ) (50a d curve c/b )
what size cable and protection will i need for d/b currently have 16mm swa feeding motors cheers all
 

Reply to cable calculation in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

The total current capacity of the system in amperes is the same as the per-phase rating when referring to a balanced three-phase system. Thus, a...
Replies
4
Views
648
  • Question
If it is TT then you can use the armour of any of them as CPC but will almost certainly need an up-front delay RCD at the sub-main feed point to...
Replies
5
Views
922

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top