cable calculation | on ElectriciansForums
Discuss cable calculation in the UK Electrical Forum area at ElectriciansForums.net
A
ample current
When you are detremining the length of a RFC what exactly is its length, is it the total amount of cable you will use or the amount you will use divided by 2?
Total length , ie , end to end measurment.
Oh, so if its say 20m to the furthest point of the circuit, the length i use for the cable calculations is 40m.
And one more question, while im on the subject, on a lighting circuit do you include all the cable drops to all the switches or just the distance to the r1+r2 point?
on lighting, you measure R1+R2 at the fitting across switch L and E with the switch closed. open the switch to confirm correct polarity.
cable calc. on RFC is R1+R2 = ( r1+r2)/4.
YES
Ignore switch drops , just measure from consumer unit to the fitting furthest away , or as you say , the R1+R2 point
Regards.
Reply to cable calculation in the UK Electrical Forum area at ElectriciansForums.net
If it is TT then you can use the armour of any of them as CPC but will almost certainly need an up-front delay RCD at the sub-main feed point to...
What kind of a socket? 13A, 16/32A commando, etc? Single socket on a radial, or multiple sockets off the same circuit?