cable calculations | on ElectriciansForums

Discuss cable calculations in the Electrical Course Trainees Only area at ElectriciansForums.net

Joined
Jan 3, 2015
Messages
348
Reaction score
35
Location
London
Hey guys just practising my cable calculations,

could you tell me if this is right I am doing it according the onsite guide as instructed in college...

this is the example


11kw oven (i know its unrealistic just making things up)
16 metres from CU
using MCB
single phase 230V
cable will be in wall plastered over for 2m then in ceiling with less then 100mm insulation for 14m.

So I calulated

Ib= 47.82A

MCB size should be = 50A

Cable size = 16mm2

Voltage drop = 2.14V

Am I correct or have I missed something out along the calculation?
 
Last edited:
way off. what about cooker diversity?

edit: unless it's an industrial oven and actually runs @ 11kW.
 
Last edited:
They work on rheostats so the element switch on and off to maintain a given temp' this gives a certain amount of diversity, it is pointless learning about it if you don't apply, if it was a shower then running it has a fixed constant load so rather than ignore diversity you should change your load in question, its a bad habit to get into and you will trip up if you done follow the correct cable calcs for the question.
 
ok firstly I done

11kw divided by 230

= 47.82A

Then since its an MCB I multiplied I by 1

= 47.82A

Went to the onsite guide table (b1 I think) and saw the appropriate MCB is 50A

Then appendix F I Saw the below 100mm insulation and it says 16mm2 when I match the 50amps to the closest value.

Then I went
 
You have got the right values.

The design current must be not greater than the rating of the circuit breaker that must be not greater than the current carrying capacity of the cable.

Ib < In < Iz

Your design current using I = P/V is 47.82 A
Circuit breakers to BS60898 come in standard ratings so a 40 A breaker would be too small but a 50A breaker correct.
The current carrying capacity of a cable varies according to the installation conditions, as more or less heat can escape the cable in different circumstance.
The current carrying capacity of a circuit is based on the most onerous conditions of installation encountered in that circuit.
You have a cable buried in plaster and a cable above a heat conductive surface (plasterboard) but covered in insulation to a depth of less than 100 mm.
The worst case is the insulation covered cable.
The standard reference method (100) for twin and earth cable installed as above gives a CCC of 45 A for 10 mm² and 57 A for 16 mm²; therefore a 16mm² cable is the smallest size that can carry the 50A current, assuming there are no other factors affecting the cable, such as ambient temperature, grouping, burial or maximum operating temperature.
 
You have got the right values.

The design current must be not greater than the rating of the circuit breaker that must be not greater than the current carrying capacity of the cable.

Ib < In < Iz

Technically that's not quite correct. Ib must be less than In and Iz, but In doesn't necessarily have to be lower than Iz in the case of fixed loads, which an oven would be.
 

Reply to cable calculations in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
348
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
888
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I can't help wondering about earthing arrangements and how important aesthetics really are when attempting to make the best of a less than ideal...
2
Replies
21
Views
1K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top