Hey guys just practising my cable calculations,
could you tell me if this is right I am doing it according the onsite guide as instructed in college...
this is the example
11kw oven (i know its unrealistic just making things up)
16 metres from CU
using MCB
single phase 230V
cable will be in wall plastered over for 2m then in ceiling with less then 100mm insulation for 14m.
So I calulated
Ib= 47.82A
MCB size should be = 50A
Cable size = 16mm2
Voltage drop = 2.14V
Am I correct or have I missed something out along the calculation?