hi, have a cable calculation question.
what size off cable do i need to run to supply a mushroom house.
its a 70 meter run of swa cable buried in the ground, the load is 12 amps lighting and sockets and a cooler taking 32 amps all this is single phase loads. there is also a 3 phase machine taking 15kw total power. can some body work this out for me show how you
work it out taking volt drop in to the equation
thanks
 
try find on site guide and is appendix 6, i9m heading for walk with kids if your still pleading , which i doubt i will help you,listen d me the spark;)
 
wolfiehogan, re your enquiry you are looking into the design & verification aspects, I will guide you as far as possible but cannot take any responsibility as I do not know the full parameters of the supply source. If we take the 2 main loads , 32 amp for cooler & 15kw total for a machine. I have assumed 15kw over the 3 phases as you have not given FLA or HP of motor. Total load on 1 phase is approx 58 amps therefore working on a 63Amp TPN supply / feed. Table 4D4a of BRB states min 16mm2. We now check volt drop, 5% of 400 =20volts max. From table 4D4B of BRB 16mm2 has volt drop of 2.4 mV/A/m, = 2.4 x 58 x 70/1000 = 9.8volts [ below 20 volts, so satisfies volt drop]. Protection for supply say 63 Amp BS88 fuse. Zs = 0.65 [ at 80% of max] therefore with a TNS supply max r1 + r2 = >0.3 ohms. From table 9A of OSG 16mm2 with 16mm2 cpc [ min due [assume presence of water supply] & to satisfy disconnection time] 2.3x 70/1000 = 0.16ohms. Zs = r1 +r2 + Ze, Zs = 0.16 + say 0.35 + 0.51, which is lower than 0.65.

Min size cable for this sinario is 4core 16mm2 swa. SWA will meet requirements as approx csa is 70mm2 which is greater than the required for a 63amp fuse. As previously stated this is aguide only. regards piccollo
 

Reply to cable calculations in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
351
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
899
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

The total current capacity of the system in amperes is the same as the per-phase rating when referring to a balanced three-phase system. Thus, a...
Replies
4
Views
659
  • Question
If it is TT then you can use the armour of any of them as CPC but will almost certainly need an up-front delay RCD at the sub-main feed point to...
Replies
5
Views
952

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top