Just seeing if im doing this correctly so im using a post from the main forum that someone has asked for help with.
cable calc for 9kw electric boiler.
cable calc for 9kw electric boiler.
This is my first post and not sure if in right place! My company have asked me to quote for a supply to be run for a 9kw electric boiler, the run will be through a ceiling void with under 100mm of insulation for about 20m, I used an online cable calc as I dont have my regs book to hand, which tells me a 16mm t +e is the minimum acceptable cable, I thought I would get a second opinion as I can imagine a 16mm is going to be extremely difficult to run through a ceiling void. Any help will be much appreciated.
Ib = 9000/230 = 39.13A
In = 40A
Iz = In/(1.00*1.0*1*0.78) = 51.28A or In/0.78 = 51.28A
So looking at Appendix F table 4D5 he would need a minimum CSA of 16mm (57A)
and the voltage drop would then be 2.8x10-3*39.13*20 = 2.19V
Only had one lesson on this so hopefully im nearly there.
Ib = 9000/230 = 39.13A
In = 40A
Iz = In/(1.00*1.0*1*0.78) = 51.28A or In/0.78 = 51.28A
So looking at Appendix F table 4D5 he would need a minimum CSA of 16mm (57A)
and the voltage drop would then be 2.8x10-3*39.13*20 = 2.19V
Only had one lesson on this so hopefully im nearly there.