Just seeing if im doing this correctly so im using a post from the main forum that someone has asked for help with.

cable calc for 9kw electric boiler.

This is my first post and not sure if in right place! My company have asked me to quote for a supply to be run for a 9kw electric boiler, the run will be through a ceiling void with under 100mm of insulation for about 20m, I used an online cable calc as I dont have my regs book to hand, which tells me a 16mm t +e is the minimum acceptable cable, I thought I would get a second opinion as I can imagine a 16mm is going to be extremely difficult to run through a ceiling void. Any help will be much appreciated.

Ib = 9000/230 = 39.13A
In = 40A

Iz = In/(1.00*1.0*1*0.78) = 51.28A or In/0.78 = 51.28A

So looking at Appendix F table 4D5 he would need a minimum CSA of 16mm (57A)

and the voltage drop would then be 2.8x10-3*39.13*20 = 2.19V

Only had one lesson on this so hopefully im nearly there.​
 
What about diversity? Need more info about the boiler, as most boilers/water heaters don't run at full load for most of the time, unlike showers. Take diversity into account and your cable CSA may well come down considerably. Without having the full design spec, an off the top of my head cable size for this would be 10mm, but it isn't clear as to whether the cable will run under or above the insulation, and even if it does, the diversity calc may still bring down your cable CSA.

Cheers............Howard

I havent checked your calcs, but they look good.
 
no. not a fixed figure like a cooker as that has several elements. your diversity estimate can only come from experience. 5 different sparks will come up with 5 different values. agree with howard. 10mm should be adequate under 4" insulation. a far better method is to route the cable above the insulation.
 

Reply to Cable calculations ? in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
351
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top