Hi Guys :yawn:
This is my understanding about the use of capping,

1. Cable Capping is not designed to protect against nails, but to protect the cable from the plasterer's trowel on traditional plastered walls and particularly aggressive lime based plasters.
Neither the steel version nor the plastic (which I will occasionally use) will protect against nails.

In fact, only steel conduit, steel trunking or SWA (steel wire armoured) cable are considered by BS7671 to offer adequate mechanical protection against nails and such like.

2. Where walls are being dabbed (or battened) and boarded on top of the cable it follows that capping is not required - I put in a enough clips to keep the cable straight and supported.

3. If I'm doing a rewire I'll cut a chase no wider than the cable and make sure it's clipped down below the surface - less work for the plasterer and less for me and less mess for the householder.

Has anyone got any problems with this?

Cheers
Pete (p'd off because on latest batten and board job, plasterer first complained about the lack of capping and then managed to put a nail straight through an armoured cable! Point made! Using a nail gun I think.)
 
Hi Guys :yawn:
This is my understanding about the use of capping,

1. Cable Capping is not designed to protect against nails, but to protect the cable from the plasterer's trowel on traditional plastered walls and particularly aggressive lime based plasters.
Neither the steel version nor the plastic (which I will occasionally use) will protect against nails.

In fact, only steel conduit, steel trunking or SWA (steel wire armoured) cable are considered by BS7671 to offer adequate mechanical protection against nails and such like.

2. Where walls are being dabbed (or battened) and boarded on top of the cable it follows that capping is not required - I put in a enough clips to keep the cable straight and supported.

3. If I'm doing a rewire I'll cut a chase no wider than the cable and make sure it's clipped down below the surface - less work for the plasterer and less for me and less mess for the householder.

Has anyone got any problems with this?

Cheers
Pete (p'd off because on latest batten and board job, plasterer first complained about the lack of capping and then managed to put a nail straight through an armoured cable! Point made! Using a nail gun I think.)
any problems with what?...
 
We always use oval conduit in Cornwall it always been the local way of doing flush work.
Conduit is normally fixed to the back of the chase with galv clout nails, at least you have some chance of rewiring, conduit is normally squashed to go into the 20mm hole, we hardly eve use capping down here
 
:yawn: When doing a rewire if capping or oval conduit was previously used you can sometimes pull the cable out and pull a new one in without having to chase the wall.:sleep1:
 
In fact, only steel conduit, steel trunking or SWA (steel wire armoured) cable are considered by BS7671 to offer adequate mechanical protection against nails and such like.

Is SWA considered to offer sufficient mechanical protection? Not that I've tried but I suspect a nail might push the strands aside and breach the armour. I recall it says the mechanical protection standard is considered difficult to meet. It's a moot point because the armour should be earthed and then it's contained in an earthed containment system which is the other way of meeting the no-RCD-needed criteria?
 
Is SWA considered to offer sufficient mechanical protection? Not that I've tried but I suspect a nail might push the strands aside and breach the armour. I recall it says the mechanical protection standard is considered difficult to meet. It's a moot point because the armour should be earthed and then it's contained in an earthed containment system which is the other way of meeting the no-RCD-needed criteria?
and for TT?
 
Capping as you point out is for protection only from the plasterer ... ps you forgot MICC on your list of mechanically protected cables, also if supplying sockets you still require RCD protection but can be afforded at the outlet provided your not abusing the exclusion regulation which in the up-coming amendments will be harder to implicate.
 
Last edited by a moderator:
bottom sentance in post #5

"It's a moot point because the armour should be earthed and then it's contained in an earthed containment system which is the other way of meeting the no-RCD-needed criteria? "

if its TT an swa would be needing an RCD...wouldn`t it....as its still may be the only way that times would be met...
 
if its TT an swa would be needing an RCD...wouldn`t it....as its still may be the only way that times would be met...

Yes but that's nowt to do with it being steel armoured, just to do with it being TT. The earthed containment the SWA provides (and the mechanical protection, if SWA is deemed mechanical protection against nails, which is what I was asking) gets you out of the need to have additional protection from an RCD what with it being buried 50mm in the wall. It can't get you out of the need to have fault protection from an RCD what with that being the only way you can meet the disco times​. Is that clearer?
 
Yes but that's nowt to do with it being steel armoured, just to do with it being TT. The earthed containment the SWA provides (and the mechanical protection, if SWA is deemed mechanical protection against nails, which is what I was asking) gets you out of the need to have additional protection from an RCD what with it being buried 50mm in the wall. It can't get you out of the need to have fault protection from an RCD what with that being the only way you can meet the disco times​. Is that clearer?
lol...you dont need to explain it to me nick....lol..

it was just where you had stated about the no RCD criteria.....so i thought i`d throw a bit of TT into the mix....lol...
 
Hi Guys :yawn:
This is my understanding about the use of capping,

1. Cable Capping is not designed to protect against nails, but to protect the cable from the plasterer's trowel on traditional plastered walls and particularly aggressive lime based plasters.
Neither the steel version nor the plastic (which I will occasionally use) will protect against nails.

In fact, only steel conduit, steel trunking or SWA (steel wire armoured) cable are considered by BS7671 to offer adequate mechanical protection against nails and such like.

2. Where walls are being dabbed (or battened) and boarded on top of the cable it follows that capping is not required - I put in a enough clips to keep the cable straight and supported.

3. If I'm doing a rewire I'll cut a chase no wider than the cable and make sure it's clipped down below the surface - less work for the plasterer and less for me and less mess for the householder.

Has anyone got any problems with this?

Cheers
Pete (p'd off because on latest batten and board job, plasterer first complained about the lack of capping and then managed to put a nail straight through an armoured cable! Point made! Using a nail gun I think.)


I don't agree with 2.

If you have more than one cable plastic capping is a lot quicker.
 

Reply to Cable Capping is NOT required and DOESN'T protect in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
801
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
833

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
947
  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top