Cable discolouration | on ElectriciansForums
Discuss Cable discolouration in the UK Electrical Forum area at ElectriciansForums.net
H
highspark
Is this an indicator that cables are overheating/first sign of deterioration?
Called out to a youth centre all upstairs lights out. Located fault a a flourescent fitting. Neutrals completely burnt out with no insulation left. I've isolated fitting. IR's are testing fine now. However I'm noticing discolouration inside the fittings of most of conductors. I am suspecting over time the insulation is going to become brittle and break away leaving exposed conductors.
Time for a rewire of circuit?
It was always customary to sleeve PVC incoming supply conductors into enclosed fittings with heat proof sleeving. I suppose that's gone by the board now in the UK, like many other good working practices!!
Sometimes, but other factors apply e.g. age and type of cable, UV exposure, contamination. You need to determine whether the cable is generally OK but deteriorating where overheated e.g. by incorrectly running past choke or high resistance connections, or generally life expired but only visibly so in the fittings. Experience needed.
It's usually still supplied in the packet with the light fitting, now whether it gets fitted or not.........
@ the OP. If the cables are testing out fine you may have a job convincing a customer that rewiring is necessary. If there is slack cable it may be beneficial to pull a few inches through and remake the connections, thereby discarding the portion of cable that has been exposed to heat. IME it's usually the connector block in fluorry fittings that crumbles before the cable insulation.
To be truthful, I can't ever remember it coming with a basic pop pack
I'm pretty certain cable deterioration could be down to the light emitted from flourescent tubes though. Not over heating.
Just look what sunlight does to cable insulation.
It's not necessarily how they look....tell more from how they feel.
Still a learner, mate ? Sorry if a bit harsh, if that's the case.
You should check how the cable feels (safely isolated of course) if it's still completely pliable and the insulation is pliable then it's probably not the heat effecting it but if it's tough and the insulation cracks it only a matter of time before the heat further damages the cable
[ElectriciansForums.net] Cable discolouration
Now this is heat-damaged insulation....
It's grey T&E btw...
Reply to Cable discolouration in the UK Electrical Forum area at ElectriciansForums.net
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Recommended Sponsor News
Hi everyone,