Today's first job.
Householder is building a retaining wall and we have lost supply on one of our street lighting cables. Inspector has done cut and test and got voltage to one point but lost it further on. No visible damage to exposed section of cable.
My job was to cut out section of cable and put in a new section. I did this and restored supply. I was determined to identify the fault in the section of cable I had removed so I kept cutting it in half and testing end to end until I had a 2 foot section left within no continuity. Then I started stripping it.
This was 6mm concentric cable and shortly after I had the live core separated . There was no visible damage, it looked perfect except about 4 inches from the end, the cable was floppy. There is a clean break in the solid aluminium conductor.
I'm assuming this is a manufacturing fault? I still have the piece in my van as evidence of what can happen in a piece of visually acceptable cable.
Any thoughts or similar experiences?
Householder is building a retaining wall and we have lost supply on one of our street lighting cables. Inspector has done cut and test and got voltage to one point but lost it further on. No visible damage to exposed section of cable.
My job was to cut out section of cable and put in a new section. I did this and restored supply. I was determined to identify the fault in the section of cable I had removed so I kept cutting it in half and testing end to end until I had a 2 foot section left within no continuity. Then I started stripping it.
This was 6mm concentric cable and shortly after I had the live core separated . There was no visible damage, it looked perfect except about 4 inches from the end, the cable was floppy. There is a clean break in the solid aluminium conductor.
I'm assuming this is a manufacturing fault? I still have the piece in my van as evidence of what can happen in a piece of visually acceptable cable.
Any thoughts or similar experiences?