No, you're right Gavin, never on a shared RCD. Most TL manufacturers will tell you that their unit exhibits about 20mA AC leakage under normal operating conditions. Odd though, that SMA "recommend" a 100mA min trip limit (to avoid nuisance tripping) and I could be mistaken but didn't P1 always recommend a 300mA trip limit, per inverter - although that could be due to the fact that most of mainland Europe (especially Germany curiously) don't consider a 100mA trip limit RCD as a standard rating, normally using either 30mA or 300mA.
So, we know in practice that a 30mA limit on a dedicated circuit is generally ok with a good quality TL unit (damp mornings are when a problem will typically materialise as we know) but on the other hand we have manufacturer's recommendations to follow....what to do? ;-)