Nuisance tripping tends to result from a combination of parasitic capacitive leakage from a floating DC array with the inherent AC leakage current from a TL inverter. If you must fit a 30mA RCD then using a TX inverter will avoid nuisance tripping.....
true, though as I say it's not been an issue once so far, and I don't expect it to be using SMA or Power-One - not so sure about the cheaper chinese models.Nuisance tripping tends to result from a combination of parasitic capacitive leakage from a floating DC array with the inherent AC leakage current from a TL inverter. If you must fit a 30mA RCD then using a TX inverter will avoid nuisance tripping.....
ask the manufacturer - power-one confirmed they don't expect to see any problems from 30mA when I challenged them on it at an installer training session, and don't have a problem with it being used as long as it's a single inverter, which it virtually always will be with a dual MPPT inverter.No, you're right Gavin, never on a shared RCD. Most TL manufacturers will tell you that their unit exhibits about 20mA AC leakage under normal operating conditions. Odd though, that SMA "recommend" a 100mA min trip limit (to avoid nuisance tripping) and I could be mistaken but didn't P1 always recommend a 300mA trip limit, per inverter - although that could be due to the fact that most of mainland Europe (especially Germany curiously) don't consider a 100mA trip limit RCD as a standard rating, normally using either 30mA or 300mA.
So, we know in practice that a 30mA limit on a dedicated circuit is generally ok with a good quality TL unit (damp mornings are when a problem will typically materialise as we know) but on the other hand we have manufacturer's recommendations to follow....what to do? ;-)
Ok. So 6mm is the way to go...
My next question is using SWA a good idea so that the cable run doesn't need RCD protection?
Depends where you're running it. Sometimes it is best to run the cable on the outside of the house (although no need to do this with a rewire - which is what I assume you are doing) If you can get the cable into the loft (or garage) without sinking the cable in then you shouldn't need SWA.
Reply to Cable from loft to CU in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net