gerard

Hi,
Just wondering if anyone knows of a gland for protecting a cable through 6-8mm thick metal? I could drill and tap ordinary glands but I have loads to do and looking for easier option. I am considering using bushings but would prefer thight fitting gland
Cheers
 
You should be able to order extended reach glands from Hawke or CMP (not sure if other makers do them, but probably they will) with a 25mm thread as opposed to 15mm.
 
If you have a load to do and its just for protection through a steel plate, have you considered using a transit frame and blocks ? On a standard 6x1 frame you can get some 48 cables of 15 mm diameter, or 24 of 24mm diameter. Otherwise if its a termination entry then you may need to consider some form of earthing the cable armouring if applicable in the enclosure (constant force springs and earth wire for example).

MCT Brattberg - Installations
 
Last edited:
Hi,
Just wondering if anyone knows of a gland for protecting a cable through 6-8mm thick metal? I could drill and tap ordinary glands but I have loads to do and looking for easier option. I am considering using bushings but would prefer thight fitting gland
Cheers

I suppose this is a silly question, but why don't you try a long reach bush and a coupler?

I think it would be the easiest and cheapest way of doing it.
 
I didn't want to use a bushing because I wanted a tight fitting that a gland gives. The machine in which the cables are located vibrates and over time it might wear into cable.
 
I didn't want to use a bushing because I wanted a tight fitting that a gland gives. The machine in which the cables are located vibrates and over time it might wear into cable.
in that case you could use a flanged bush with a lead washer (they come with a long-reach bush)

I worked on a fisheries protection vessel in shipyard in North Devon.
terminating 2x star-delta motors just outside the engine room, I found that the gland plate was about 10mm thick.
The first hole I drilled in at the motor.
The other 3 I drilled on a pillar drill in a workshop.
I know there is alot of vibration in 38 meter Naval vessel and it was acceptable there.
 
The cable was connected to a motor that moves and I was concerned about the constant movement. Observed it working and it seems fine. All good now thanks!
 

Reply to Cable glands for thick metal sheet in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

Sounds more positive.
Replies
8
Views
472
  • Question
Bulk buy a load of cheap white plastic switches and sockets until plaster is dry and decorating has been carried out so you dont have to worry...
Replies
4
Views
1K
  • Question
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Replies
5
Views
581
Sorry, 3. Should read: separate circuit from consumer unit with 16amp radial supply only to this lighting/camera…
Replies
1
Views
1K
  • Question
Especially as Friday is normally dedicated to liquid.
Replies
11
Views
7K
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks