SSE
As above, is there a reg that actually tells you a maximum size of cable allowed per depth of box or is it just a guideline used? ie Max for 25mm, 35mm, 45mm depth of metal back boxes?
Reg 522.8.1 A wiring system shall be selected and erected to avoid during installation, use or maintenance, damage to the sheath or insulation of cables and their terminations.
Think this one could apply to shallow back boxes being used on heavier cables.
Reply to Cable Maximums For Back Boxes in the Australia area at ElectriciansForums.net
Good question now to start with thermosetting insulated conductors are not tri-rated that is something different. Table 4E1A deals with this type...
An example of the long term race to the bottom of quality of work in our industry, IMHO.