hi just been to look at a job, have to get a cable accross 4 joists ( perpendicular) now i know drilling loft joists is a no no, the cable run will be in an area of the loft not used for storage and the customer has no intention to board out the loft is there anything wrong with laying the cables accross the joists, neatly and secured under the existing insulation? ( 1.5mm 6amp lighting)
 
yes i know its in the book is that for floor and loft joists ?? im not totally sure it is. i guess it depends on the size of the joist in the loft space.

i cant really see any problem with laying over the joist as in a non traffic area and customer is not boarding the loft
 
I'd venture to suggest that going through the odd joist is better, especially if some muppet comes along with boards later and traps the cable between the joist and the board!
 
thats my preferred option to be honhest just wasnt sure just looked in the building regs for electricians and it states the hole/span sizes are for both roof and floor joist i guess its wheather a roof joist = loft joist. confusing
 
Notching and/or drilling ceiling and floor joists are both allowed under the Building Regulations Part A.
Notching joists in top edge only, in the zone 0.07 to 0.25 of the span, maximum size 0.125 x depth of joist.
Drilling joists on the centre line only, in the zone 0.25 to 0.4 of the span, maximum size 0.25 x depth of joist, holes in the same joist should be at least 3 diameters apart.
No notches or holes should be cut into roof rafters, other than at supports where the rafter may be birdsmouthed to a depth not exceeding 0.33 x rafter depth.
See EGBR 2.3.2 and 10.1.1 for details.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
cable run perpendicular to loft joists.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
16
Unsolved
--

Advert

Thread statistics

Created
ianphilip007,
Last reply from
DaveyD,
Replies
16
Views
7,365

Advert

Back
Top