Hi wondering if anyone has any advice on what type of cable would be best.

I need to run a 600amp 3 phase feed with neutral using single core with power lock connectors for just under 50meter across the open floor with short sections in cable ramp, from this it will be broken down into 3x 125amp 3 phase connectors each taking just under 100amp per phase.
This will feed some 3 phase equipment and also break down into several single phase supplies.
For shorter runs of this I have used H07RNF at 120mm, but wondering on sizing for this length run and if there are alternatives to H07RNF that would give us the same current capacity still be flexible enough to move and keep with in our voltage drop.
Thank for any help.
 
The OP has asked a question there is no need to drill him over his qualifications. The offending and now not relevant posts are gone.
 
No offence taken quite happy to be asked. my questions is more of a general enquiry, in case I have missed a type of cable that could be use. Your link to the cleveland trirated is for panel wiring cable is this not really suitable for laying on the ground in exposed areas?
 
Glad you understand but these questions can quickly throw a thread off course and at times stop new members pursuing the thread.
Yes tri rated conductors would require additional protection.
 
You need to do some calculations taking volt drop into consideration but it will be 500 to 630mm. I would suggest contacting Cleveland or Eland cables for an accurate sizing.
 

Reply to cable selection 600amp 3 phase in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
295
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
277
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
354

Similar threads

When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
3K
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
926

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

  • exceeding voltage drop
    The cable is way undersized. If the voltage drop is detrimental to the installation I would make...