Can someone please help me with calculating the cable size of a 50kw 3-phase Ac supply over 35m, on cable tray using swa? Just need to know the cable calculation as im getting confused.
Regards
Volt drop for solar should be no more than 1%.
Volt drop in volts is mV/A/m * A * m / 1000
Calculate your amps from I = P / V or I =
Distance is 35m
mV/A/m values are given in table 4D4B in BS7671
Reply to Cable sizing 50kw solar system in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
The total current capacity of the system in amperes is the same as the per-phase rating when referring to a balanced three-phase system. Thus, a...
If your using 35mm or 50mm use 2 core SWA and use the armour as the earth, it'll cut down on price. I know people will comment on this but the...