Hi all, I know it's hard to tell without seeing a job but, we're wanting to put some camping pods in at one of our sites. We're only looking at basic electrics, LED lighting and a couple of sockets for phone charging but no heaters as they won't be used all year round. We considered 16A caravan hook up points but I think we'd rather wire them direct. There will be 5 of them at 16A so total load would be 80A and the length of cable will need to be about 140metres. The cable will be SWA buried underground. Someone said they had worked out that the cable size would need to be 35mm because of the voltage drop on that length of cable, it seems kind of big to me but it's not my area so thought I'd ask those in the know. Thanks
Multicore 90°C Armoured Thermosetting Insulated Cables​
Tables Apply to: H6942XL, H6943XL, H6944XL, H6945XL, Tuff Sheath,
Voltage:230V
Load:18.4kW / 80A
Length:140m
Method of Installation direct in ground or in ducting in ground
Cable Size:50mm²
I’d advise getting an electrician involved. They will know to add diversity to your calculation, which means your 16A times 5 pods won’t actually need 80A
You say no heating, but what about appliances that heat, such as kettles?
Without any high load, and it’s just lighting and chargers, tv, etc…. They won’t pull 6A never mind 16
And also it's a distributed load, so only the incoming section of cable takes full load, and each sequential section takes correspondingly less. Does reducing cable size along the run help cost, or just complicate the job?
Reply to Cable sizing for camping pods in the UK Electrical Forum area at ElectriciansForums.net
To be honest James I use an app- Electrical Calculations. It auto calculates the cable size once you enter the specifics/parameters. Voltage...
Thanks for that guys I was more thinking about difference in potential between the tub and wet paving flags . The tub is plastic . But it’s the...