Morning....
I was wondering if you guys could help me with this..?!
I’m currently having my kitchen updated, including all new appliances...
The oven, according to the manufacturers documentation has a rating of 4.2kw, which is 2.2kw or the oven and 2.2kw for the grill... The paperwork states it requires a 20a supply...
I’m site based, and don’t have much to do with domestic installations generally, now obviously 4.2kw equates to 18.26a...
The run of cable is approximately 5 metres from the DB, and doesn’t travel through any thermal insulation as it’s surface mounted (mt2) high level in the conservatory and then back entry though the wall to pick up the oven (sounds worst than it actually is)...
Now please excuse my ignorance, but would you guys wire this with a 2.5mm t&e on a 20a breaker to a 20a double pole switch..?! (obviously with 30mA protection coming from the split load board).... Or would this be better on a 4.0mm t&e fed via a 20a breaker..?!
Any help would be very very much appreciation...
I was wondering if you guys could help me with this..?!
I’m currently having my kitchen updated, including all new appliances...
The oven, according to the manufacturers documentation has a rating of 4.2kw, which is 2.2kw or the oven and 2.2kw for the grill... The paperwork states it requires a 20a supply...
I’m site based, and don’t have much to do with domestic installations generally, now obviously 4.2kw equates to 18.26a...
The run of cable is approximately 5 metres from the DB, and doesn’t travel through any thermal insulation as it’s surface mounted (mt2) high level in the conservatory and then back entry though the wall to pick up the oven (sounds worst than it actually is)...
Now please excuse my ignorance, but would you guys wire this with a 2.5mm t&e on a 20a breaker to a 20a double pole switch..?! (obviously with 30mA protection coming from the split load board).... Or would this be better on a 4.0mm t&e fed via a 20a breaker..?!
Any help would be very very much appreciation...