Morning gents, just a quick one. I've posted this already on the Solar PV forum but thought I'd add it here too as VD and cable calcs are always a good topic of discussion.
So I have a Solar PV system to install this weekend, its a 10KW single phase system on a farm. I'm going to be running a 2-core SWA from the substation to the invertor, the cable is going to be buried and as you know there needs to be <3% VD. My cable calculations are coming back with results of up to 95mm for some reason, this can't be correct surely? Any constructive help would be much appriciated, Cheers, Lee
 
Last edited:
Shouldn't you be aiming for a volt drop of less than 1% as per the "Guide"? (page 44, section 2.3.1):

"The a.c. cable connecting the inverter(s) to the consumer unit should be sized to minimise voltage
drop. A 1% drop or less is recommended. However in larger installations this may not be practicable
or economic due to the very large size of cable resulting. In this case the designer should minimise
voltage drop as far as possible and must remain within voltage drop limits as prescribed by BS 7671.

Note: The recommendation for a 1% voltage drop is due to two reasons: firstly when generating,
the voltage at the inverter terminals is higher than the voltage at the supplier’s cutout – during
periods of high power output this voltage drop must be kept to a minimum in order to prevent the
inverter nuisance tripping on over voltage ; secondly the requirement ensures losses from the PV
system are minimised."

You could have a play with SMA's Sunny Design which may be helpful in determining the correct cable for your situation.
 
Shouldn't you be aiming for a volt drop of less than 1% as per the "Guide"? (page 44, section 2.3.1):

"The a.c. cable connecting the inverter(s) to the consumer unit should be sized to minimise voltage
drop. A 1% drop or less is recommended. However in larger installations this may not be practicable
or economic due to the very large size of cable resulting. In this case the designer should minimise
voltage drop as far as possible and must remain within voltage drop limits as prescribed by BS 7671.

Note: The recommendation for a 1% voltage drop is due to two reasons: firstly when generating,
the voltage at the inverter terminals is higher than the voltage at the supplier’s cutout – during
periods of high power output this voltage drop must be kept to a minimum in order to prevent the
inverter nuisance tripping on over voltage ; secondly the requirement ensures losses from the PV
system are minimised."

You could have a play with SMA's Sunny Design which may be helpful in determining the correct cable for your situation.

ideally yes, but the 1% is merely a recommendation. Lee
 
70mm spot on for 10kW single phase, we've had to run that before now, Try running it three phase 4 core, that's fun getting around corners, up stanchions and across portal frames :)

You will suffer continuous disconnects if you go for the 3% and clinet will be seriuusly p***d off with output during the peak production times.

We know, we had the DNO screw up with voltages on one site, so they gave us written direction to reconfigure a 50kW system to G83, else it would have cost them an arm and a leg in new transformers - the local one was already down at the lowest tapping, upstream was the problem..
 

Reply to Cable sizing solar PV in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Bear in mind if you get a company to install this then the battery would of course be vat free aswell. Flux is an intersting tariff but also...
Replies
1
Views
1K
  • Question
Hi Dave, I did a reply last night, but the system would not let me post it! I was not logged in and then it lost everything I had typed. It was...
Replies
6
Views
3K
Bury a 4 inch duct under the pathway with drawropes until the time they are needed and pull in the correct size of cable at the time. We would...
Replies
1
Views
713
Good Morning All! Always appreciate reading the great ideas and conversations in the forums, and now actually have a chance to ask a question...
    • Like
Replies
0
Views
997
Hi, Similar'ish question to my other thread but little more info now so a different approach but sorry if duplication. UK, single phase. Just had...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks