"A cable complying with the appropiate standard having a non-metallic sheath or a non metallic enclosure is deemed to provide satisfactory protection against both direct and indirect contact, as does an item of class II equipment. Class II equipment is constructed such that any insulation fault in a cable cannot result in a fault current flowing into any conductive parts with which the equipment may be in contact. Hence the metal cable tray or basket need not be earthed."
This doesn't make any sense.
Firstly,
"A cable complying with the appropiate standard having a non-metallic sheath or a non metallic enclosure is deemed to provide satisfactory protection against both direct and indirect contact, as does an item of class II equipment"
OK fair enough, twin and earth cable is similar to Class II equipment
"Class II equipment is constructed such that any insulation fault in a cable cannot result in a fault current flowing into any conductive parts with which the equipment may be in contact"
EH? So if the cable insulation fails for whatever reason, it is impossible for the metal cable tray that it is cable tied to to become live? WTF?!!
I'm pretty certain that if a line voltage is applied to a metal cable tray, then that cable tray will become live. Cos it's made of metal.
"Hence the metal cable tray or basket need not be earthed."
Maybe it NEED not be earthed, as a piece of twin and earth is regarded as Class II equipment (
????) , but to me that is sailing close to the wind. As I've SEEN a ceiling grid become live as a result of a fault , I am gonna ignore the advice from GN8 and I will earth both the tray and the grid.