Currently reading:
Cables buried in wall less than 50mm UK
Discuss Cables buried in wall less than 50mm UK in the UK Electrical Forum area at ElectriciansForums.net
Could somebody please clarify a certain aspect of this for me? I have posted in the IET forum and got no reply.
So say you install cables in a wall/partition less than 50mm below the surface. You run the cables in the specified zones and you protect it with a 30ma RCD.
Do you still need to use earth armouring, earthed metal sheath or earthed steel conduit? Or is the RCD sufficient?
Reg 522.6.204 of BS 7671:2018 seems to state it is not.
I'm studying to do the latest regs and was under the impression cables were permissible at a depth of less than 50mm as long as they we're protected by RCD 30ma. Is this now not the case with the new regs (18th edition). Do they need this mechanical protection too?
[automerge]1588514851[/automerge]
No need to answer this I have found the answer. Guidance notes 3 clearly states that a RCD 30ma is sufficient protection.
It is clearly worded, unlike the regs, the on-site guide
and the explained illustrated 18th Edition Wiring Reg books, which are very unclear and seem to be missing an OR from their wording which would clearly indicate this to be the case. Well that was 2 hours of study time wasted!
The regs used to be very clear on this point, can you post an image of the regulation which you feel is unclear? I don't have a regs book to hand at the moment.
regs. are unclear in my view. have a look at 522.6.202
this implies that cables can be run anywhere , diagonal or out of zones as long as said cable/s comply with 522.6.204.
doesn't help when you have to turn the page between the relevant regs.
That has got to be the most ridiculous criticism of the regulations I have seen yet.
How self entitled do you have to be to want everything put on one page for you? What do you expect them to do print them all on one damn page or maybe supply a slave to turn the pages for you?
You in a bad mood Dave? :D
So the confusion came from here;
Reg 522.6.201 says (i.) Less than 50mm deep use the 150mm from ceiling and horizontal/ vertical runs.
(ii) Complies with reg 522.6.204
I took this as both requirements for indents needed to be met
and when you go to reg 522.6.204 it says the cable shall; then goes to list the mechanical protection and selv/pelv.
I took this as it it need to comply with both, but reading again i see that the note beneath 522.6.201 says "Where (i.) applies but not (ii) cables shall be provided with RCD".
Not very clear at all!
So i went to the onsite guide and it has a list;
A cable installed in a wall or partition must. Then it goes onto list the requirements a, b c, d.. Each of these option has an or after it except after the RCD.
Which makes it sound like it's an additional requirement to one of the rest.
So luckily GS3 states in plain and simple! But thanks for all your replies, I've had nothing from the IET forum still!
(Just tried to upload pics from each book, but they've fail to upload!)
Reply to Cables buried in wall less than 50mm UK in the UK Electrical Forum area at ElectriciansForums.net