I have a machine fed with singles in trunking, 3 phase, all test out ok, short run but cables are getting very warm, unit has a motor which also tests ok .
Any ideas????
 
flc 12.5A
sc 30A
DOL with 14-21 o/l
Sorry Johno missed your post.Installation is about 8y old with no probs.
There is an identical motor 3m shorter that is no probs.
Done all the normal stuff just looking for one of those daft faults you sometimes come across.
The heat of the cable is causing the o/l to trip!!!
 
Last edited:
Are all the connections tight and clean, is the gearbox or whatever it is driving in good nick, not binding or anything? Simple stuff I know and i dont wish to insult your intelligence but sometimes we look too deep.

Cheers........Howard
 
Hi,

Could the motor be wired incorrectly, if it was wired in delta and should be in star this would cause twice the current to flow:eek:

just a thought
 
What do you mean by 'half load'?

The thread is going along the lines of just having a motor on a 3 phase supply, but obviously that is not the case.

What is the machine you are referring to?
 
i assume he means half-capacity( 12amp on 2.5 )

cables hot,overload is tripping -they're drawing a lot more than that

mechanical issue
check wiring
 
Last edited by a moderator:
Thanks guys been on hol ,
In no particular order,
problem is with 1 dol motor on a large (ish)paint plant unit.
singles in trunking then kopex
cables clamped at o/l giving 12.5 11.9 12.3 A
fitter has removed motor and checked says ok
unit has been installed for 8 years no props
re checked terms etc all ok windings all ok
half load being i dont expect 2.5 to get hot (60deg) at 12.5 A
 

Reply to cables getting hot on half load in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

I see no issue with this, it sounds like a relatively normal installation. The use of insulated and sheathed cables inside steel trunking is a...
Replies
5
Views
228
davesparks
D
Sounds more positive.
Replies
8
Views
474
  • Question
This UK company seem to sell parts for them so it might be worth contacting them after that you could try the manufacturers La Rocca | Máquinas de...
Replies
1
Views
785
  • Question
That looks like a Metrel display (I have one), they have a permanent 3 wire display that measures the three combinations so I would say that’s a...
Replies
5
Views
645
I can imagine it just disappearing (loudly) under short circuit conditions, then the resulting blast/plasma etc. casing the busbars to flash over...
Replies
13
Views
574

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks