I am on a job at the moment and we are pulling 12 4mm's down 25mm conduit?This can't be right.It is so tight.What should be the limit?
 
I would say the conduit space fator is by far exceeded, I'm amazed you can physically get them in there!!

There are calcs you can do to confirm, you'll find the factors in BS 7671 or the OSG.
 
Last edited by a moderator:
I'm allways a little confused by this 45% rule.
How does it explain capping or tubing running in walls supplyling ring mains, they are filled to well over 45%.
And oval running from light switches up the walls to the lights, they are filled easily more than 45%.
What about the conduit supplying the fuse board? That's usually full to bursting.
But the most common one I see is oval running from the light switch up the wall behind the plaster filled with lighting cables.
Who really obeys this 45% rule?
 
Not the most reliable source but one of my college tutors reckoned it was physically impossible to get enough cables in a conduit to exceed the maximum capacity.
With capping or oval conduit one side of each of the cables is likely to be in contact with the plaster, which I would have thought would dissipate some of the heat.
 
was on a subbing job once in a hospital. 6 x 4mm low smokes down 20mm tube. had to get 1lb of lard from hospital kitchen
 

Reply to Cables in conduit? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
706
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
970

Similar threads

Good question now to start with thermosetting insulated conductors are not tri-rated that is something different. Table 4E1A deals with this type...
Replies
1
Views
280
If you get a length of conduit, and seal both ends then the IP rating will instantly be IP68!! If you buy an IP66 rated Wiska box it will...
Replies
10
Views
666

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top